<html>
<body>
Colleagues:<br><br>
I had posted earlier that I was having problems reliably starting a
particular generator using an Outback Mate.&nbsp; My resolve was to
determine conclusively if the Outback mate was at fault or if I could
trust it in the future.&nbsp; I installed a data monitoring system to
check battery voltage, gen start signal and gen AC waveform and briefed
the care taker and staff to scrutinize the system carefully during the
test period.&nbsp; Here are the results:<br><br>
There were 4 generator start failures over a period of about 4 weeks.
Failure numbers 1 and 3 were verified to have been caused by the
generator.&nbsp; Failures 2 and 4 were due to failure of the customer to
reset the Mate after failures 1 and 3.&nbsp; This was a training error
that was partly mine.&nbsp; <u>No failures can be blamed on the Outback
equipment.<br><br>
</u>Moral of the story:&nbsp; Generator start systems are
complicated.&nbsp; You need to know your generator and your customer
needs to know his or her Mate.&nbsp; But, the Mate AGS works.<br><br>
More information:<br><br>
The Kohler RES 15 displays numerals under normal circumstances and alpha
characters under abnormal circumstances.&nbsp; I posted a note in the
generator shed informing anyone that if alpha characters are seen, to
note the characters, time, date and then to call me.<br><br>
The Mate is difficult enough for the technician to understand.&nbsp; My
customer has an elderly caretaker for whom English is a second
language.&nbsp; After I discovered the training error, I created a few
flip charts with lots of graphics and copies translated into Spanish,
followed up by on-site training.&nbsp; This should prevent repeats of the
failure to clear AGS Errors.&nbsp; This highlights the industry wide
problem of systems having too complicated a front end.<br><br>
Data monitoring proved the point that generator failure was the original
culprit.&nbsp; If anyone is interested in more information about a
roll-your-own low-budget data monitoring system, I created a page on the
subject:&nbsp;
<a href="http://millersolar.com/case_studies/Data/data.html" eudora="autourl">http://millersolar.com/case_studies/Data/data.html<br><br>
</a>I firmly believe that third party generator start hardware adds an
unnecessary level of complication and removes the added feature of tieing
generator stop to the float stage.&nbsp; I will continue to use and
recommended the Outback integrated AGS system.<br><br>
William Miller<br><br>
<br><br>
<x-sigsep><p></x-sigsep>
<font size=3><u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</font></body>