<i>From what I've been told the fire was located in one of<br>
the combiner boxes. It started as they were commissioning the system.
We<br>
had completed our final inspection and their electrical contractor had
done<br>
an insulation resistance test on all conductors.&nbsp; No modules were
involved.<br>
Ground faults do not appear to be the cause of the fire but there is
a<br>
possibility of miss marked and/or installed positive/negative 
output<br>
conductors. The system design has three 12 string combiners per&nbsp;
pull box.<br>
There are approximately 2,500 modules total for the 650 kW system.
The<br>
engineering team at Bright Power is currently investigating the cause
of<br>
the fire. I'll let you know what they discover.<br><br>
<br><br>
<br>
</i>At 05:17 PM 11/14/2010, you wrote:<br>
<blockquote type=cite class=cite cite>I have searched the net and cannot
find any photos of this fire damage, or any report that explains the
damamge in detail.&nbsp; What about the installer?&nbsp; Have they
stepped up to investigate, or perhaps the fire marshall?&nbsp;&nbsp; When
these things happen everybody heads to their corners, but we all would
benefit from good information about these kinds of &quot;what not to
do&quot;.<br>
&nbsp;<br>
Anybody on the list near there and might have more iinfo?<br>
&nbsp;<br>
&nbsp;<br>
Jeff Yago<br><br>