<font size=3>Eric:<br><br>
Thanks for the research.&nbsp; I confess that I commented on an inverter
system I knew little about.&nbsp; My thanks to Darryl for keeping me
honest, and for the kind words.&nbsp; I had assumed that all modern
inverters are certified to prevent back feed, but this needs to be
checked for each new inverter.<br><br>
I'm not sure the language below is the same as an independent
verification that back feed will not occur.&nbsp; You may need to ask
your AHJ what they will accept.<br><br>
The limit on allowable back current is the fuse sizing specified by the
module manufacturer.&nbsp; This relates to how much fault current the
internal module wiring can handle before it fails (and possibly catches
fire).<br><br>
Humbly,<br><br>
William Miller<br><br>
<br><br>
<br><br>
At 07:42 PM 11/14/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Thanks William and Daryl,<br><br>
Here is Auroras backfeed stipulation from the installation
manual:<br><br>
&quot;Installation and Operators Manual Page 98 of 108<br><br>
(PVI-3.0/3.6/4.2-OUTD-x-US Rev: 2.1)<br><br>
<b>8.5 Input Source Backfeed Current</b><br><br>
PVI-4.2(3.6, 3.0)-OUTD-x-US Grid Tied Inverters are provided with two
separate and<br>
consecutive power stages:<br><br>
 Booster Stage (DC-DC converter) connected to DC Input Terminals.<br>
 Inverter Stage (DC-AC converter) connected to AC Output Grid
Terminals.<br><br>
The Booster Stage is provided with forward diodes that allows the current
(power)<br>
flow only from DC Input terminals towards Inverter (Output) Stage.<br>
In case of any fault on Inverter Stage, these diodes avoid any back-feed
current<br>
phenomena towards input terminals.<br><br>
In case of fault of the forward diode, the corresponding booster MOSfet
goes<br>
immediately and permanently in short circuit state and it avoids any
current<br>
propagation form output to input terminals.<br><br>
Abnormal Fault tests conducted during UL1741 qualification show also that
these type<br>
of faults produce the opening of internal grid disconnect relays and
cause the external<br>
AC CB protection devices to trip, preventing any power flow from the
grid.<br><br>
In conclusion for PVI-4.2(3.6, 3.0)-OUTD-x-US-y models it is not possible
to have<br>
any single fault responsible of Input source back-feed current flow. For
these models<br>
the Back-feed current into DC Source is negligible.&quot;<br><br>
According to this, the inverter will not backfeed even under most fault
conditions. My biggest concern is the four independent strings shorting
together somehow. I guess technically 4 strings of 8A for a total of 32A
doesn't exceed the ampacity of 10AWG XHHW-2....until you derate it for
roof temps. <br><br>
So whats the consensus?<br><br>
-- <br>
Eric Thomas<br>
Solar Epiphany LLC<br>
(206) 919-3014<br>
<a href="http://www.solarepiphany.com">www.solarepiphany.com</a><br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.449 / Virus Database: 271.1.1/3257 - Release Date: 11/14/10
19:34:00</blockquote>
<x-sigsep><p></x-sigsep>
<u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</font></body>
</html>