Gilligan,<br><br>
Below is the data you asked for:<br><br>
A)&nbsp; Measure and Record DC Voltage between Positive and Negative
(VOC).&nbsp;&nbsp;&nbsp; <font color="#0000FF"> 0.0 to 0.1<br>
</font>B)&nbsp; Measure and Record DC Voltage between Positive and
Ground.&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
<font color="#0000FF">0.0 to 0.1<br>
</font>C)&nbsp; Measure and Record DC Voltage between Negative and
Ground.&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
<font color="#0000FF">503 VDC<br><br>
</font>No sign of rain.&nbsp; <br><br>
No evidence of a ground fault.&nbsp; If a fault exists, it is
intermittent.&nbsp; The system worked fine for a week with the new
inverter.&nbsp; Since it went down, I've done repeated checks and found
no evidence of a fault.&nbsp; Fortunately the system is close by.
<br><br>
There is one string of 10, Sanyo 210s.&nbsp; The installation is 9 months
old.&nbsp;&nbsp; The only J-Box is in the attic and is dry and wired very
cleanly.&nbsp; The system worked great until a few weeks ago.&nbsp;
<br><br>
I will check the rotation of wheel on the meter again, when we get the
GFP fuses in.&nbsp; I think the inverter was producing power.&nbsp;
<br><br>
No Spark on the DC wires.&nbsp; <br><br>
Note:&nbsp; The first inverter did NOT blow the GFP fuse.&nbsp; I worked
intermittently.  <br><br>
Has anyone had problems with Sanyo modules faulting?&nbsp; <br><br>
Thanks,<br><br>
Drake <br><br>