William,<br>
<br>
There are some issues with putting the charge controller at the other
end of the feeder:<br>
1. The advantage of a higher voltage feeder is lost.<br>
2. The voltage drop in the feeder will mess up the charge controller's
absorption and float set points.&nbsp; Say there is only 1% drop in the
deeper, that's 0.14 volt for a 12 volt system (2x for 24 or 4X for 48
volts).&nbsp;&nbsp; If the feeder loss is more ...&nbsp; You could raise the set
points at the regulator to offset the feeder loss, but the loss in the
feeder is not a constant.<br>
3. The charge controllers are not NEMA 3 rated, they need to be inside.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>
<br>
<br>
<br>
<br>
William Miller wrote:
<blockquote cite="mid:6.0.1.1.2.20101020083650.03788ea0@millersolar.com"
 type="cite"><font size="3">Jay:<br>
  <br>
Bad idea.&nbsp; The differences in tolerances within components will make
one work harder than the other.&nbsp; They will never balance.&nbsp; Why
not put the charge controllers at the other end of the feeder?<br>
  <br>
William Miller<br>
  <br>
  <br>
  <br>
At 08:06 AM 10/20/2010, you wrote:<br>
  </font>
  <blockquote type="cite" class="cite" cite=""><font size="3">HI All,<br>
    <br>
Say anyone ever paralleled mx/fm-60's?<br>
    <br>
I have a unique situation that would be very expensive to pull
additional
wire however the existing wire is large enough to need 2 fm-60s'<br>
    <br>
If I put a diode between them so they don't feed each other any
problems
that anyone knows of?<br>
    <br>
thanks,<br>
    <br>
jay<br>
    </font></blockquote>
  <pre wrap="">
  </pre>
</blockquote>
</body>
</html>