class=765193713-12102010>Well yes but, 690.64 (2) is titled and reads "Bus or 
Conductor Rating". The "or" is important and the 120% requirement does not apply 
to the upstream conductors, in this case.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=765193713-12102010></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=765193713-12102010>In general, if the&nbsp;sudpanel of 225A where backfeed 
with the 120A of PV and had a 150A breaker&nbsp;on its&nbsp;feeder from the main 
panel, the conductor between the main panel and the sub need be rated only for 
the 150A feeder conductor.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><SPAN class=765193713-12102010><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=765193713-12102010><FONT color=#0000ff 
size=2 face=Arial>The size of the feeder tap between the transfer switch lug and 
the new sub panel needs to be evaluated differently.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=765193713-12102010><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=765193713-12102010><FONT color=#0000ff 
size=2 face=Arial>I myself am a big fan of 240.21 (B), even when it comes to 
feeders with PV on them. I guess some folks are not, but other than the 
expression of opinion, I don't see anything to prohibits the use of downsized 
feeder taps in PV circuits. I think most folks would go for a downsized 
conductor to connect up the new subpanel, so long as it was located right next 
to the transfer switch equipment.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><BR><SPAN lang=en-us><FONT size=2 face=Arial>Mark 
Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley Solar 
Electric Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>303 
Redbud Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada 
City,&nbsp; CA 95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>(530) 401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial>&nbsp;</FONT></SPAN> </DIV>
<DIV>&nbsp;</DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Jason 
Szumlanski<BR><B>Sent:</B> Tuesday, October 12, 2010 4:05 AM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Supply side connection to a 
dedicated panel<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>That sounds right, which means that the existing wiring between the service 
disconnect and the transfer switch may also need to be evaluated since it will 
now have sources available at both ends. The rule applies to all bus bars and 
conductors "upstream" of the interconnection point &nbsp;as I understand 
it.<BR><BR>Jason Szumlanski</DIV>