<div><div>Dave,<div><br></div><div>I think you are reading the output current for 277V. The spec sheet lists AC max output at 240V as 7700W and 32A. If you take that number at face value, you can still just use a 40A breaker. If you do the math based on their listed output (7700W/240V=32.1A * 1.25 = 40.1A), you might need to bump up to a 45A breaker; probably depends on the comfort level of you as the installer and the AHJ inspecting.</div>

<div><br></div><div>For your main breaker or fuses, I think you could use 125A no matter how you interpret the required sizes of the inverter breakers; just don&#39;t round up to the next breaker/fuse size until after you have done your calculations for all three inverters. 7700W * 3 / 240V * 1.25 = 120.3A, so round up to 125A for the breaker size. Your new total input would be 125A+135A = 260A, which leaves you at the same place: 225A panel based on a b+w reading of 690.64, or a broader interpretation and therefore a smaller panel?<br>

<br></div><div><div>Around the Bay Area, there are some places that would not let us use the dedicated panel idea, because it is not spelled out clearly in NEC. Other AHJs are fine with it, especially with permanent signage installed stating something about &#39;for combining inverter output circuits only, do not connect additional loads&#39;, etc. If you are a strict code-stitutionalist and go with the bigger 225A panel, don&#39;t forget that the code reads &#39;bus bar and conductors&#39;, applying to the conductors in between your combiner panel and your point of connection.</div>

<div><br></div><div>I&#39;ve had a few drawn out discussions with John Wiles on this issue, and he always encourages me to use the bigger panel--we do sometimes, not always. Someone here.... maybe Bill?.... has mentioned a push to get the inverter combiner panel exception written into NEC, but no luck yet.</div>

<div><br></div><div>Then there is the issue about if the line side of the ATS is rated for you to tap/lug on, but I&#39;m glad you didn&#39;t ask about that one ;)</div><div><span class="Apple-style-span" style="font-family: arial, sans-serif; font-size: 13px; border-collapse: collapse; "><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">

</p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><a name="12947529a5c408e2__MailAutoSig" style="color: rgb(0, 0, 204); "><span style="font-size: 10pt; ">Phil Boutelle</span></a><span><span style="font-size: 10pt; "></span></span></p>

<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span><span style="font-size: 10pt; ">Project Engineer<br>NABCEP Certified Solar PV Installer<sup>TM</sup><br>Real Goods Solar, Inc.</span></span></p>

<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span><span style="font-size: 10pt; "></span></span><span><span style="font-size: 10pt; color: blue; "><a href="http://www.iesolar.com/" target="_blank" style="color: rgb(0, 0, 204); ">www.RealGoodsSolar.com</a></span></span></p>

<div><span><br></span></div></span></div></div></div><div class="gmail_quote">On Mon, Oct 11, 2010 at 9:14 PM, Dave Palumbo <span dir="ltr">&lt;<a href="mailto:dave@independentpowerllc.com" target="_blank">dave@independentpowerllc.com</a>&gt;</span> wrote:<br>


<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">








<div lang="EN-US" link="blue" vlink="purple">

<div>

<p class="MsoNormal">We are installing a 8kW grid tied PV system for a commercial
client. There is an auto start generator on the premises, therefore we
will be utilizing a supply side AC point of connection. Inverter is an SMA
SB8000. System owner plans on adding to system in the next few years. We are
designing for a total of 24kW of PV.</p>

<p class="MsoNormal"></p>

<p class="MsoNormal">We will install a 200A fused disconnect off the grid feed (line
side of the generator transfer switch). My plan is install a dedicated breaker
panel for the inverter 240VAC output(s). The SB8000 is rated at 29 Amps, so a
40A DP breaker will do for the point of connection. This panel will eventually
have a total of (3) 40A DP breakers each with 8kW of inverter output. </p>

<p class="MsoNormal"></p>

<p class="MsoNormal">My question has to do with the interpretation of the 120
percent rule of the rating of the busbar in the panel. Do I need to use a 225
Amp rated panel with a downsized 150A main breaker? 225A busbar x 1.2 = 270
Amps -150A MB = 120A total of inverter output allowed. Or, since this panel
will only be used for inverter AC point of connection, and not for loads, is it
allowable to label this panel as a Dedicated Panel  connect no
loads. If that is the case we could use a 200A panel, or even a 150Amp
panel. A local electrician proposed this dedicated panel to avoid
the larger load center panel. I cannot find any mention of dedicated
panel in the NEC. </p>

<p class="MsoNormal"></p>

<p class="MsoNormal">I think what I am proposing follows 690.64. Any opinions, or
advice would be appreciated.</p>

<p class="MsoNormal"></p>

<p class="MsoNormal">Dave Palumbo</p>

<p class="MsoNormal">Independent Power LLC </p>

<p class="MsoNormal"><i><a href="http://www.independentpowerllc.com" target="_blank">www.independentpowerllc.com</a> </i></p>

<p class="MsoNormal">NABCEP Certified PV Installer</p>

<p class="MsoNormal">Vermont Solar Partner</p>

<p class="MsoNormal">802.888.7194 </p>

<p class="MsoNormal"></p>

<p class="MsoNormal"></p>

<p class="MsoNormal"></p>

<p class="MsoNormal"></p>

<p class="MsoNormal"></p>

</div>

</div>


<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>