<DIV dir=ltr align=left><SPAN class=868314517-14092010>Stir 
away....</SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010>Modern locking module 
connectors serve as DC disconnects for micro-inverters.&nbsp;This point&nbsp;was 
alluded to in the Code Corner sidebar, but not addressed in detail. 
I</SPAN><SPAN class=868314517-14092010>t takes a little dance&nbsp;along Route 
690 to drive the point home to OCD-afflicted AHJs... But it's right 
there...</SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010>The simplest dance steps 
generally start with 690.14(A). This clause specifically says disconnects don't 
have to be&nbsp;suitable as service equipment and must comply with 
690.17.</SPAN><SPAN class=868314517-14092010>&nbsp;690.17&nbsp;requires 
disconnects to be manually operable switches or breakers that meet a host of 
requirements. And then there's the exception, which throws all that out the 
window... Or off the roof, as the case might be. </SPAN><SPAN 
class=868314517-14092010><EM>(Exception: A connector shall be permitted to be 
used as an ac or a dc disonnecting means, provided that it complies with the 
requirements of 690.33 and is listed and identified for the use.)</EM> Listed 
and identified as a PV connector meets this requirement. </SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=868314517-14092010>As your AHJ is quivering 
with OCD discomfort... Quickly flip to 690.33 to send him/her into full-on 
convulsions... </SPAN></DIV>
<DIV>&nbsp;</DIV>
<DIV><SPAN class=868314517-14092010>690.33 requires connectors to be polarized, 
noninterchangeable with other stuff on the premises, guarded live parts, 
latching or locking, require a tool to open, 1st make/last break grounding 
member and... Either be rated for interrupting current without hazard to the 
operator OR require a tool to open and marked "Don't open under load". 
</SPAN></DIV>
<DIV><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV><SPAN class=868314517-14092010></SPAN><SPAN 
class=868314517-14092010>Demonstrate your compliance to the AHJ this way: Flip 
your module over, grab both connectors, plug them into each other, yank on the 
wires to demonstrate that a tool is required to open the connector, and flick 
the sticker-tape labels that say "Do Not Disconnect Under Load". Hand the 
connection to your AHJ. Make hm or her check it out closely. While he/she is 
examining the connection, reconciling in their own head&nbsp;the irrational 
concept that a disconnect doesn't have to be a switch here.... Turn the module 
to face the sun and point out to them that they are now holding an energized 
dead short. Just for fun :)</SPAN></DIV>
<DIV><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV><SPAN class=868314517-14092010>If they can't wrap their head around the 
concept, take them over to your work truck. Pull out a skilsaw. Show them the 
nameplate amps and discuss the power of the tool.&nbsp;Way more watts and 
higher&nbsp;voltage&nbsp;than your module.&nbsp;Carry the thing over to a live 
receptacle, plug it in, squeeze and hold the trigger, pull the plug out of the 
receptacle. Happens every day with all kinds of tools and appliances. 
</SPAN><SPAN class=868314517-14092010>There's no label on the cord or receptacle 
to say you can't... </SPAN><SPAN class=868314517-14092010></SPAN></DIV>
<DIV><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV><SPAN class=868314517-14092010>Now compare this to your module connectors 
to demonstrate how much safer and more effective the locking, labeled connectors 
are. Buried up there behind the modules and all. Where only a qualified person 
can get to them. Where, in the event of an emergency, shutting down the ac 
circuit reduces the&nbsp;maximum potential current to one module. No matter how 
bad the fault is or where it's located. Which is the lowest possible unit of 
energy in a modern PV system. Can't get much safer than that!</SPAN></DIV>
<DIV><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV><SPAN class=868314517-14092010>Hope it didn't take too long to fall 
asleep...</SPAN></DIV>
<DIV><SPAN class=868314517-14092010></SPAN>&nbsp;</DIV>
<DIV><STRONG><I><SPAN 
style="FONT-FAMILY: 'Monotype Corsiva'; mso-bidi-font-family: Tahoma">Matt 
Lafferty</SPAN></I></STRONG></DIV>
<DIV class=Section1>
<P class=MsoNormal><SPAN style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"><A 
href="mailto:gilligan06@gmail.com">gilligan06@gmail.com</A></SPAN></P></DIV>
<DIV><SPAN class=868314517-14092010>&nbsp;</SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of 
</B>SOLARPRO@aol.com<BR><B>Sent:</B> Tuesday, September 14, 2010 10:19 
AM<BR><B>To:</B> re-wrenches@lists.re-wrenches.org<BR><B>Subject:</B> 
[RE-wrenches] DC Discos for Enphase<BR></FONT><BR></DIV>
<DIV></DIV><FONT id=role_document color=#000000 size=2>
<DIV>Howdy Wrench<SPAN class=868314517-14092010>&nbsp;&nbsp;</SPAN></DIV>
<DIV>I don't try to stir things up, but I was just wondering last night as I 
fell asleep reading the latest issue of HomePower magazine (# 139), if anybody 
else caught a chill when they read this in the Code Corner (highlighted in a 
box):</DIV>
<DIV>&nbsp;</DIV>
<DIV>"Both microinverters and microinverters attached to PV<BR>modules in the 
field or in the factory that have any exposed<BR>DC single conductor cables are 
required to meet all of the<BR>NEC&#8217;s DC wiring requirements. These may include 
Section<BR>690.5 ground-fault detector requirements, DC and AC<BR>disconnect 
requirements (potentially handled by connectors<BR>listed as disconnects), and 
inverter DC grounding-electrode<BR>requirements."</DIV>
<DIV>- John Wiles</DIV>
<DIV>&nbsp;</DIV>
<DIV>&nbsp;Which begs the question: Are &lt;any&gt;&nbsp;module connectors 
currently&nbsp;listed as disconnects?</DIV>
<DIV>&nbsp;As well as: If DC voltages for each disconnect are less than 48 
V,&nbsp;would a simple&nbsp; switch suffice, should the poor hapless installer 
run into an AHJ with OCD?&nbsp;&nbsp;&nbsp;&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV><FONT lang=0 size=3 PTSIZE="12" FAMILY="SANSSERIF">Patrick A. 
Redgate</FONT><FONT lang=0 color=#000000 size=2 PTSIZE="10" 
FAMILY="SANSSERIF"><BR><B><I>AMECO Solar, Inc.<BR>Serving Solar 
California<BR>Since 1974<BR>7623 Somerset, Blvd.<BR>Paramount, CA 
90723<BR>562-633-4400<BR></B></I><A 
href="http://www.solarexpert.com/">www.solarexpert.com</A><U><BR><A 
href="http://www.amecosolar.com/">www.amecosolar.com</A><BR><BR></U></FONT></DIV></FONT></BODY></HTML>