Citel products do have a listing mark but this is European style CE, not American style UL/ETL. Citel is reputedly working on American certification but one would be advised to not hold one&#39;s breath.<div><br></div><div>

The Citel products which mount to a DIN rail have an LED indicator which goes dark once the surge elements have beensacrificed. Also some of their units have an auxiliary switch which can remotely indicate a blown condition. This is in the form of dry contacts..a normally open and a normally closed one, so various indicator circuits can be designed around that. The contacts have a low amp AC rating and also a (lower amp) DC rating but I do not remember the numbers at present.</div>

<div><br></div><div>Jolliness,</div><div><br clear="all">Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">On Tue, Sep 14, 2010 at 12:43 PM, R Ray Walters <span dir="ltr">&lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">

<div style="word-wrap:break-word">You could buy several ground rods for the cost of one Delta.<div>Ground Impedance is the real issue. Both the Delta and the Polyphasor need a good ground to work.<div>While I haven&#39;t seen much of a correlation between Deltas and reduced lightning damage, (lots of system damage with and without)</div>

<div>I have found that well grounded systems (tied to a steel cased well) have never had a problem, even with direct strikes to a wind turbine (did lose the $40 turbine rectifier, but nothing else)</div><div><br></div><div>

I now own a clamp-on ground impedance tester, and the results were miserable. Some electrodes were over 800 ohms to ground! (code requires under 25 ohms)</div><div>I&#39;d spend more time and money reducing ground impedance, and then if it makes you feel good inside, throw the little &quot;lightning faeries&quot; in, if the AHJ isn&#39;t looking.......</div>

<div><br></div><div>If its really lightning country, and a really expensive off grid system,I use Polyphasor, but they have their own issues. (very expensive, no UL listing, loose internal connections, nuisance tripping, need a large J-box to mount them inside, etc.)</div>

<div>I haven&#39;t tried the Citel stuff, but it looks to be listed, and mounts on a DIN rail. After installing a couple hundred Deltas, I&#39;d try something else at this point.</div><div><br></div><div><br><div>
<span style="border-collapse:separate;border-spacing:0px 0px;color:rgb(0, 0, 0);font-family:Helvetica;font-size:12px;font-style:normal;font-variant:normal;font-weight:normal;letter-spacing:normal;line-height:normal;text-align:auto;text-indent:0px;text-transform:none;white-space:normal;word-spacing:0px"><div>

R. Walters</div><div><a href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a></div><div>Solar Engineer</div><div><br></div><div><br></div><br></span>
</div><div><div></div><div class="h5">
<br><div><div>On Sep 14, 2010, at 10:22 AM, Kristopher Schmid wrote:</div><br><blockquote type="cite">
<div>
<div><span><font face="Arial" color="#0000ff" size="2">My 
thought here is that nothing will protect the equipment from a direct strike, 
but a near strike that may induce a significant surge may be absorbed by the LA 
and protect the equipment. I like the feedback so far. It would not 
break my heart to stop using them altogether.:-}</font></span></div>
<div><span><font face="Arial" color="#0000ff" size="2"></font></span></div>
<div><span><font face="Arial" color="#0000ff" size="2">Kris</font></span></div><p><font size="2">Legacy Solar<br>864 Clam Falls Trail<br>Frederic, WI 
54837<br>715-653-4295<br><a href="mailto:solman@legacysolar.com" target="_blank">solman@legacysolar.com</a><br><a href="http://www.legacysolar.com" target="_blank">www.legacysolar.com</a> 
</font></p>
<blockquote style="margin-right:0px">
  <div></div>
  <div lang="en-us" dir="ltr" align="left"><font face="Tahoma" size="2">-----Original Message-----<br><b>From:</b> 
  <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a> 
  [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>August 
  Goers<br><b>Sent:</b> Tuesday, September 14, 2010 10:39 AM<br><b>To:</b> 
  RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] Delta 
LAs<br><br></font></div>
  <div>All -</div>
  <div></div>
  <div>I guess my thought is a little off topic, but are lightning arrestors 
  even worth using at all? My logic has always been that if lightning does 
  indeed strike that it&#39;s likely going to blow the arrestor and and inverter. We 
  don&#39;t have much of a lightning issue issue in the Bay Area so I don&#39;t have any 
  direct experience.</div>
  <div></div>
  <div>Best,</div>
  <div></div>
  <div>August<br><br></div>
  <div class="gmail_quote">On Tue, Sep 14, 2010 at 6:29 AM, Kristopher Schmid 
  <span dir="ltr">&lt;<a href="mailto:solman@legacysolar.com" target="_blank">solman@legacysolar.com</a>&gt;</span> 
  wrote:<br>
  <blockquote class="gmail_quote" style="padding-left:1ex;margin:0px 0px 0px 0.8ex;border-left:#ccc 1px solid">It 
    is quite ironic that just a week after I posted a question to the 
    group<br>on testing the integrity of lightning arrestors, I had one 
    apparently faulty<br>out of the box. The manifest of this was 
    interesting: when the AC LA<br>(LA302R) was connected in parallel on the AC 
    input to a SB3000 inverter,<br>there was 125vac neutral to L1, 125vac 
    neutral to L2, and 1Vac L1 to L2.<br>SMA tech support suggested the LA as 
    the issue and sure enough, it was.<br>Attempting to test good and faulty 
    arrestors with an ohmmeter gave the same<br>result - off scale 
    open.<br><br>Any thoughts or comments from the group?<br><br>Kris 
    Schmid<br><br>Legacy Solar<br>864 Clam Falls Trail<br>Frederic, WI 
    54837<br>715-653-4295<br><a href="mailto:solman@legacysolar.com" target="_blank">solman@legacysolar.com</a><br><a href="http://www.legacysolar.com/" target="_blank">www.legacysolar.com</a><br><br>_______________________________________________<br>

List 
    sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Options 
    &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: 
    <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List 
    rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out 
    participant bios:<br><a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br><br></blockquote></div><br><br clear="all"><br>-- <br>August Goers<br>VP, Engineering<br><br>Luminalt Energy 
  Corporation<br>1320 Potrero Avenue<br>San Francisco, CA 94110<br>O: 
  415.641.4000<br>M: 415.559.1525<br><a href="mailto:august@luminalt.com" target="_blank">august@luminalt.com</a><br></blockquote></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>

Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>

<br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>

<br></blockquote></div><br></div></div></div></div></div><br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div>