<html>
<body>
<font size=3>Colleagues:<br><br>
I have been saying for some time that we need to rethink PV ground fault
indicator systems.&nbsp; The fundamentals of existing GFI systems is for
the bond between the grounded-conductor and the&nbsp; grounding-conductor
to be opened upon a ground fault.&nbsp; This bond is important for safety
and it is ludicrous to open it at the time it is most needed.<br><br>
There are patents awarded for systems to detect ground faults and then
disconnect PV source circuits at the source.&nbsp; This is the best idea
I can think of at this time.&nbsp; There are more patents to be had for
those that can innovate in this area.&nbsp; Until there are better
systems on the market, regulators can not require better
alternatives.<br><br>
William Miller<br><br>
<br><br>
<br>
At 01:04 PM 9/6/2010, you wrote:<br><br>
</font><blockquote type=cite class=cite cite><font face="arial" size=2 color="#0000FF">Wrenches
all,<br>
</font><font size=3>&nbsp;<br>
</font><font face="arial" size=2 color="#0000FF">I 100% second Bill B's
comment Correct that... I 200% second it. It should be the law....
<i>&quot;Don't begin to troubleshoot a faulted PV circuit without a
reliable DC clamp meter.&quot;<br>
</i></font><font size=3>&nbsp;<br>
</font><font face="arial" size=2 color="#0000FF">The <b>MOST
DANGEROUS</b> <b>PV system</b> is a wounded PV system. This includes
danger to persons and property. Safely and efficiently troubleshooting a
faulted PV circuit requires a voltmeter AND an ammeter. And PPE. And
adequate knowledge and understanding of operational and non-operational
characteristics of PV systems.<br>
</font><font size=3>&nbsp;<br>
</font><font face="arial" size=2 color="#0000FF">The simple reason for
this is that, when one or more circuit conductors are faulted to a short
condition, the voltage between the faulted elements is zero. Relying on
just a voltage reading to determine whether or not to open a circuit
under this condition will result in an arc. The amount of energy in that
arc will depend on the amount of available sunlight and the amount of PV
that is feeding into it. The amount of potential hazard will correspond
to these factors as well.<br>
</font><font size=3>&nbsp;</font></blockquote></body>