<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial,helvetica,sans-serif;font-size:12pt">HI Wrenches:<br>&nbsp;&nbsp;&nbsp; My crew wants to nail all the flashings on our footings, but I am resisting.&nbsp; Do you guys have any strong feelings about that.<br><div>&nbsp;</div>Nick Soleil<br>Project Manager<br>Advanced Alternative Energy Solutions, LLC<br>PO Box 657<br>Petaluma, CA 94953<br>Cell:   707-321-2937<br>Office: 707-789-9537<br>Fax:    707-769-9037<div><br></div><div style="font-family: arial,helvetica,sans-serif; font-size: 12pt;"><br><div style="font-family: arial,helvetica,sans-serif; font-size: 10pt;"><font size="2" face="Tahoma"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Bob-O Schultze &lt;bob-o@electronconnection.com&gt;<br><b><span style="font-weight: bold;">To:</span></b> RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<br><b><span style="font-weight:
 bold;">Sent:</span></b> Tue, July 27, 2010 7:04:36 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [RE-wrenches] AL wire with DC<br></font><br>
Agreed with Dick on this one. First, if you are going the DB route, then you have to get it down at least&nbsp; 24" instead of 18". No problem some places, a HUGE problem others. Then there are the burrowing critters like ground squirrels which love to chew on anything. I have heard that there is something put into the insulation which makes it distasteful, but I sure don't believe it- if true.<br>Bob-O<br><br>On Jul 27, 2010, at 4:06 AM, Richard L Ratico wrote:<br><br>The insulation on Al cable rated for direct burial is thick and tough. But,<br>DON'T direct bury it. Carefully pull it into correctly installed PVC conduit.<br>Use marker tape above the conduit, just below grade.<br><br>If you're in an area that doesn't experience ground frost, MAYBE, VERY<br>CAREFULLY, plant the cable in a generous amount of sand. If you're in an region<br>with frost, ALWAYS use conduit. <br>I think it is false economy to skip the conduit. The sand application is
 very<br>time consuming. <br><br>Buried copper wire with nicked insulation may not turn to dust, but is certainly<br>a MAJOR bummer, particularly if it's not in conduit, AND, it's at least 3X the<br>cost of Al. Al, done right, no worries.<br><br>Dick Ratico<br>Solarwind Electric <br><br>--- Drake wrote:<br>Aluminum wire got its bad name during the era when it was use in 15 <br>and 20 amp circuits, with #12 and #10 wire.&nbsp; That stuff is a <br>nightmare.&nbsp; As an electrician that has cleaned up some of the messes, <br>I can supply ample horror stories.<br><br>#2 and larger sizes of AL work fine.&nbsp; It is important to use <br>antioxidant on the connections.&nbsp; Separate copper wire from aluminum <br>using a listed splicing device.<br><br>Aluminum wire will turn to white powder in an underground cable where <br>the insulation has been breached.&nbsp; This is true for DC or AC.<br>_______________________________________________<br>List sponsored
 by Home Power magazine<br><br>List Address: <a ymailto="mailto:RE-wrenches@lists.re-wrenches.org" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><span><a target="_blank" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><br><span>List-Archive: <a target="_blank" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><br>List rules &amp; etiquette:<br><a target="_blank" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a target="_blank" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br><br></div></div>
</div><br>

      </body></html>