Try tweaking upward on the voltage at which the system disconnects from gen. I can&#39;t remember exactly in the Mate where that is found...&quot;AC Input&quot; may be the heading.<br><br>I believe the preset for that is 108 volts per leg or other fairly low number. If the inverter stack waits for the generator AC to collapse to such a low level before doing the transfer, that may be why the loads you mention are acting strangely. <br>

<br>Jolliness,<br><br clear="all">Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">On Mon, Jun 14, 2010 at 11:31 PM, William Miller <span dir="ltr">&lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">


<div>
<font size="3">Wrenches:<br><br>
I have a customer that has a problem with a new generator. He has
two VFX3648 inverters in Outback stacking. He acquired a new
generator, a Kohler 12RES, a reputable make and model. Below is a
description of the problem:<br><br>
</font><font size="2" face="arial"><i>The 12RES seems to be operating OK
except for one problem. At the end of a charging cycle, when the
gen automatically shuts down and load goes back to the inverters, all
lights, TVs, etc., flash, one TV shuts off, and a GFI trips. This
has happened every time. It did not happen with the 15RES or the
smaller back-up gen (which was disconnected manually). With the
15RES the same GFI would occasionally trip while the unit was charging
and handling house load, but never at the auto shutdown point. I
replaced the GFI, but it still trips. There are three GFIs in the
house, but only one--always the same--trips.<br><br>
<br>
</i></font><font size="3">I suggested he adjust the AC2/Gen transfer delay
to a lower number. He reduced it to minimum and this did not
resolve the problem. I also had him verify that the AC source is
selected as generator, which it is.<br><br>
Do you have any suggestions?<br><br>
Thanks in advance,<br><br>
William Miller<br><br>
<br>
<p>
<u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: <a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a><br>
<a href="http://millersolar.com/" target="_blank">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</p></font></div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>