<font face="Verdana">Nick,<br>
<br>
Sorry for the delayed reply.&nbsp; I've been traveling and am just catching
up on e-mails.<br>
<br>
Your method is absolutely correct.&nbsp; We're working on an appnote and a
calculator to provide you guys with some quick tools.<br>
<br>
David also brings up a favorite technique of mine.&nbsp; When you center
feed the branch, the reduction of voltage rise is significant.&nbsp; Cutting
the # of inverters in half cuts the voltage drop to 1/4.&nbsp; It also
reduces the power loss in the branch wiring to 1/4 of the end-fed value.<br>
<br>
A couple of examples (which use the M190 and the current 14awg wiring)
will demonstrate.&nbsp; This is at full power for a 240vac split-phase
circuit, and the current is 0.8Aac.&nbsp; These calcs also include contact
resistance of the connectors:<br>
<br>
If you put 15 inverters on one branch circuit and they are end-fed, the
last inverter will see a voltage rise of 4.2 volts (1.75%).&nbsp; If you put
15 inverters (the max. allowed on one dedicated OCPD), split 7 and 8
per side, the last inverter on the side with 8 inverters will see a&nbsp;
1.3 volt (0.54%) rise.&nbsp; Acceptable in most cases.<br>
<br>
If you must end-feed, a branch of 15 inverters will see a rise of 4.2
volts </font><font face="Verdana">(1.75%) </font><font face="Verdana">and
the end, but a branch of 10 inverters will only see a rise of 1.9 volts
(0.8%) at the end.&nbsp; Again, acceptable in most cases.<br>
<br>
Ultimately, by center feeding a branch of 14 inverters, the end
inverters will see less than a 1 volt (0.42%) rise.&nbsp; If this is not
acceptable, there are other problems.<br>
<br>
Of course, you must also add the voltage drop for the feeder to the PV
sub panel, and any wiring from the sub panel to the first pigtail in a
branch to arrive at the voltage at the PCC.<br>
<br>
Please note that we are not accounting for terminations in the sub,
breaker losses, sub panel losses, intermediate connections, etc.&nbsp; These
can add a few tenths of a volt.<br>
<br>
We are going to 12AWG wire in the upcoming Trunk and Drop wiring
system, which some of you have already previewed.&nbsp; This will allow a
20A OCPD, but will be limited by all of the same Physics that apply to
the existing wiring system.&nbsp; We just can't seem to get around that
Physics thing.<br>
<br>
I hope this helps!<br>
</font>
<pre class="moz-signature" cols="72">See ya!

Marv
707 763-4784  x7016
</pre>
<br>
<br>
David Brearley wrote:
<blockquote
 cite="mid:C83800ED.8B1F%25david.brearley@solarprofessional.com"
 type="cite">
  <title>Re: [RE-wrenches] AC wiring loss on micro-inverters</title>
  <font face="Calibri, Verdana, Helvetica, Arial"><span
 style="font-size: 11pt;">Maybe Marv can help out here. I&#8217;ve talked
with tech support at Enphase and am under the impression that you can
center tap their branch circuits to reduce voltage drop. This technique
was used on a project that we profiled in SolarPro:<br>
  <br>
  <a moz-do-not-send="true"
 href="http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1&amp;search=">http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1&amp;search=</a><br>
  <br>
David Brearley, Senior Technical Editor<br>
  <i>SolarPro</i> magazine <br>
  <br>
  <br>
On 6/11/10 2:50 PM, "Nick Soleil" &lt;<a moz-do-not-send="true"
 href="nicksoleilsolar@yahoo.com">nicksoleilsolar@yahoo.com</a>&gt;
wrote:<br>
  <br>
  </span></font>
  <blockquote><font face="Arial"><span style="font-size: 12pt;">Did you
notice that in my calculation I divided the total amperage by 2 to get
the average ampacity across the string. &nbsp;This seems to be the best way
to deal with that. &nbsp;Otherwise the loss would have been over 2.8%<br>
&nbsp;<br>
Nick Soleil<br>
Project Manager<br>
Advanced Alternative Energy Solutions, LLC<br>
PO Box 657<br>
Petaluma, CA 94953<br>
Cell: &nbsp;&nbsp;707-321-2937<br>
Office: 707-789-9537<br>
Fax: &nbsp;&nbsp;&nbsp;707-769-9037<br>
    <br>
    <br>
    </span></font><font face="Tahoma, Verdana, Helvetica, Arial"><span
 style="font-size: 11pt;">
    <hr align="center" size="1" width="100%"><b>From:</b></span><font
 size="2"><span style="font-size: 10pt;"> "<a moz-do-not-send="true"
 href="markf@berkeleysolar.com">markf@berkeleysolar.com</a>" &lt;<a
 moz-do-not-send="true" href="markf@berkeleysolar.com">markf@berkeleysolar.com</a>&gt;<br>
    <b>To:</b> RE-wrenches &lt;<a moz-do-not-send="true"
 href="re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
    <b>Sent:</b> Fri, June 11, 2010 7:02:00 AM<br>
    <b>Subject:</b> Re: [RE-wrenches] AC wiring loss on micro-inverters<br>
    </span></font></font><font size="2"><span style="font-size: 10pt;"><font
 face="Arial"><br>
Nick,<br>
    <br>
Good to see other wrenches looking at this issue. &nbsp;However, remember
that<br>
in the interconnect cable between the last and the second to last
Enphase,<br>
the current is small. If you really want to see how the loss is adding
up<br>
you need a more detailed analysis that averages the voltage drop for the<br>
entire system of interconnect cables.<br>
    <br>
Mark Frye<br>
Berkeley solar Electric Systems<br>
    <br>
&gt; Hello wrenches and Marv:<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;How many Enphase inverters do you put on a single parallel
string?<br>
&gt; The Enphase manual allows for up to 15, but I have found that a
single<br>
&gt; string of 15 can have very high voltage rise on the AC wiring. &nbsp;Up
to<br>
&gt; 1.5% loss just on the Enphase cables, and that does not take into<br>
&gt; account resistance at the plug connectors or any home-run wiring.<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;15 inverters x 190 watts = 2850 watts<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;2850 watts / 240 Volts = 11.875 Amps (however at the beginning
of the<br>
&gt; string it is 0 Amps)<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;length of contacts + internal wiring = ~6'<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;Total Enphase cabling length (6' x 15 inverters) = ~90'<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss<br>
&gt; It is pretty hard to design for 1.5% voltage &nbsp;drop if you have to
size for<br>
&gt; 0% loss on your wiring! &nbsp;I hope Enphase will increase the size of
the wire<br>
&gt; in their cables soon. &nbsp;Have you experienced issues with
micro-inverters<br>
&gt; shutting off due to high AC voltages?<br>
&gt;<br>
&gt; &nbsp;Nick Soleil<br>
&gt; Project Manager<br>
&gt; Advanced Alternative Energy Solutions, LLC<br>
&gt; PO Box 657<br>
&gt; Petaluma, CA 94953<br>
&gt; Cell: &nbsp;&nbsp;707-321-2937<br>
&gt; Office: 707-789-9537<br>
&gt; Fax: &nbsp;&nbsp;&nbsp;707-769-9037<br>
&gt;<br>
&gt;<br>
&gt;<br>
&gt;<br>
&gt; ________________________________<br>
&gt; From: i2p &lt;<a moz-do-not-send="true" href="i2p@aol.com">i2p@aol.com</a>&gt;<br>
&gt; To: RE-wrenches &lt;<a moz-do-not-send="true"
 href="re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
&gt; Sent: Thu, June 10, 2010 4:50:47 PM<br>
&gt; Subject: Re: [RE-wrenches] Real world PV production<br>
&gt;<br>
&gt;<br>
&gt;<br>
&gt; On Jun 10, 2010, at 7:57:53 AM, "Kelly Keilwitz, Whidbey Sun &amp;
Wind"<br>
&gt; &lt;<a moz-do-not-send="true" href="kelly@whidbeysunwind.com">kelly@whidbeysunwind.com</a>&gt;
wrote:<br>
&gt;<br>
&gt; PV Watts VASTLY underestimate PV production<br>
&gt;&gt; &nbsp;in our area.<br>
&gt; PV Watts underestimates in Central Ca too.<br>
&gt;<br>
&gt; Don<br>
&gt;<br>
&gt;<br>
&gt; &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;_______________________________________________<br>
&gt; List sponsored by Home Power magazine<br>
&gt;<br>
&gt; List Address: <a moz-do-not-send="true"
 href="RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;<br>
&gt; Options &amp; settings:<br>
&gt; <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;<br>
&gt; List-Archive:<br>
&gt; <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
&gt;<br>
&gt; List rules &amp; etiquette:<br>
&gt; <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a> &lt;<a moz-do-not-send="true"
 href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>&gt;
    <br>
&gt;<br>
&gt; Check out participant bios:<br>
&gt; <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a> &lt;<a moz-do-not-send="true"
 href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>&gt;
    <br>
&gt;<br>
&gt;<br>
    <br>
    <br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
    <br>
List Address: <a moz-do-not-send="true"
 href="RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
    <br>
Options &amp; settings:<br>
    <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
    <br>
List-Archive: <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
    <br>
List rules &amp; etiquette:<br>
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
    <br>
Check out participant bios:<br>
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a> &lt;<a moz-do-not-send="true"
 href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>&gt;
    <br>
    <br>
    </font></span></font><font face="Calibri, Verdana, Helvetica, Arial"><span
 style="font-size: 11pt;"><br>
&nbsp;<br>
    <hr align="center" size="3" width="95%"></span></font><font size="2"><font
 face="Consolas, Courier New, Courier"><span style="font-size: 10pt;">_______________________________________________<br>
List sponsored by Home Power magazine<br>
    <br>
List Address: <a moz-do-not-send="true"
 href="RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
    <br>
Options &amp; settings:<br>
    <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
    <br>
List-Archive: <a moz-do-not-send="true"
 href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
    <br>
List rules &amp; etiquette:<br>
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
    <br>
Check out participant bios:<br>
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
    <br>
    </span></font></font></blockquote>
  <font size="2"><font face="Consolas, Courier New, Courier"><span
 style="font-size: 10pt;"><br>
  </span></font></font><font face="Calibri, Verdana, Helvetica, Arial"><span
 style="font-size: 11pt;"><br>
  <br>
  </span></font>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
</blockquote>
</body>
</html>