<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;">Hi fellow wrenches forgive me if this has been said. <br>The AC is a special problem on MIcro inverters because the long runs modules to service are now in the AC section of the system.&nbsp; The DC connections are very short.&nbsp; The utility has a +- 5% normal tolerance, which leaves us with only 5% to count on.&nbsp; If the grid is high any voltage rise would put us very close to high voltage shut down.&nbsp; The manufacture is trying to help us prevent nuisance shut downs, and is looking for 1% voltage rise.&nbsp; Voltage rise or drop is easily calculated in English units by Vr=2KIL/CM where K is the coefficient of resistance for copper (12.9)&nbsp; I is the current in amps, (0.82x#of M190 inverters) L is the one way length of the wire run.&nbsp; or equally straight forward is Vr= 2LIR/1000 where the L is the one way length, I is the current as above, R is
 the resistance per 1000 feet of wire.&nbsp; The CM and R values are from Chapter 9 Table 8 of the NEC <br>Darryl<br><br>--- On <b>Fri, 6/11/10, Jeff Yago <i>&lt;jryago@netscape.com&gt;</i></b> wrote:<br><blockquote style="border-left: 2px solid rgb(16, 16, 255); margin-left: 5px; padding-left: 5px;"><br>From: Jeff Yago &lt;jryago@netscape.com&gt;<br>Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters<br>To: kirk@vtsolar.com, "RE-wrenches" &lt;re-wrenches@lists.re-wrenches.org&gt;<br>Date: Friday, June 11, 2010, 5:42 PM<br><br><div id="yiv1211728287"><div style="font-family: Arial,sans-serif; font-size: 10pt;"><div>I just attended a training class in Philly last week by Enphase technical staff and my notes say they suggest up to 15 micro-inverters @ 190 watts each per string with no problem.&nbsp; They also are now shipping their dual module micro-inverter which should help with this wire issue since this model #D380 has two #M190 units built
 into the same box which is only slightly larger than&nbsp;a single micro-inverter.</div>
<div>&nbsp;</div>
<div>Since this new dual micro-inverter does NOT have the AC pass-through wire built-in, you are no longer limited to the wire size that comes in and out for the 240 VAC connections.&nbsp; HOWEVER, they require you to purchase this awful looking multi-tap pigtail cable for the AC connections which has a pre-wired connector spaced the expected distance apart the micro-inverters would be installed, and this is a $950 item for every six dual micro-inverters.&nbsp; When I saw this thing I thought is was a python that had swalled six pepsi cans!&nbsp; Not sure what this will look like on a roof or how well it can be hidden behind the array, but it uses a larger wire size so perhaps the wire loss issue has been resolved.</div>
<div>&nbsp;</div>
<div>Jeff Yago</div>
<div>DTI Solar</div><br>&nbsp;<br><hr>Netscape.&nbsp; Just the Net You Need.</div>
</div><br>-----Inline Attachment Follows-----<br><br><div class="plainMail">_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a ymailto="mailto:RE-wrenches@lists.re-wrenches.org" href="/mc/compose?to=RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div></blockquote></td></tr></table><br>