<font size=3>Kent:<br><br>
Good points.&nbsp; Enphase may allow us to disconnect their DC connectors
under load, but each of their connectors mates with a connector installed
at the PV factory.&nbsp; The module makers usually say don't disconnect
under load.&nbsp; So the inverter and the PV listings both need to allow
disconnecting.<br><br>
William Miller<br><br>
<br><br>
At 08:49 PM 5/20/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Marv,<br><br>
The manual now clearly states that the ac and dc connectors have been
evaluated and approved for use as the required ac load break
disconnect.&nbsp; Yet in other locations the manual still says
&quot;Never disconnect the DC wire connectors under load&quot; and
&quot;The AC connector of the first microinverter in a branch circuit is
suitable as a disconnecting means once the AC branch circuit breaker in
the load center has been opened.&quot;<br><br>
Sorry, but that's just not a clear a set of instructions yet.&nbsp; Can
we open these connectors under load or are we never supposed to open them
under load?<br><br>
Kent Osterberg<br>
Blue Mountain Solar<br>