<html>
<head>
<style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Verdana
}
--></style>
</head>
<body class='hmmessage'>
Thanks for sharing that Dana,<div><br></div><div>Are you required by code or the AHJ,&nbsp;for micro-inverter systems,&nbsp;to have an additional AC d/c aside from the branch circuit breaker? (on the roof or other location)</div><div><div><br></div><div>For these micro-inverter systems the only&nbsp;labeling&nbsp;required&nbsp;here,&nbsp;by&nbsp;code (CEC), is;</div><div>84-030&nbsp;(1) which states... &nbsp;&nbsp;</div><div> A warning notice of an interconnected system shall be installed in a conspicuous place at the supply authority disconnecting means of Rule 84-022 and the supply authority meter location.</div><div><br></div><div>84-022 is generally referring to the load center main breaker. &nbsp;And the utility company puts their own "WARNING: interconnected system" label at the meter.</div><div><br></div><div>So we don't 'have to' provide any additional info, but i think that providing some is a good idea. As Ray pointed out, too much info can be discouraging.</div><div>&nbsp;</div><div>For now, I have opted for these labels on the load center as the only labeling for the system;</div><div>Code required -- "WARNING Two Power Source Parallel System" and;</div><div>Optional for info --&nbsp;"Grid-Connected Solar Electric System</div><div><span class="Apple-tab-span" style="white-space:pre">  </span>&nbsp;&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;Array Rating: 660 WDC</div><div><span class="Apple-tab-span" style="white-space:pre">        </span>&nbsp;&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;Module Rating (each): 220 WDC"</div><div>....the optional one will of course need to be replaced and updated if/when the owner decides to add to his system.</div><div><br></div><div>cheers,</div><div>benn</div><div><br><span class="ecxecxecxEC_Apple-style-span" style="color:rgb(0, 32, 96)">DayStar Renewable Energy Inc.&nbsp;</span><div><div>benn@daystarsolar.ca</div><div>780-906-7807&nbsp;</div><div>HAVE A SUNNY DAY


</div><div><br></div></div><br><br><hr id="stopSpelling">From: dana@solarwork.com<br>To: re-wrenches@lists.re-wrenches.org<br>Date: Mon, 17 May 2010 14:29:12 -0600<br>Subject: [RE-wrenches] Enphase System Labeling<br><br>






<style>
.ExternalClass p.ecxMsoNormal, .ExternalClass li.ecxMsoNormal, .ExternalClass div.ecxMsoNormal
{margin-bottom:.0001pt;font-size:12.0pt;font-family:'Times New Roman','serif';}
.ExternalClass a:link, .ExternalClass span.ecxMsoHyperlink
{color:blue;text-decoration:underline;}
.ExternalClass a:visited, .ExternalClass span.ecxMsoHyperlinkFollowed
{color:purple;text-decoration:underline;}
.ExternalClass p
{margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:'Times New Roman','serif';}
.ExternalClass span.ecxecxecxecapple-style-span
{;}
.ExternalClass span.ecxEmailStyle19
{font-family:'Century Gothic','sans-serif';color:windowtext;font-weight:normal;font-style:normal;text-decoration:none none;}
.ExternalClass .ecxMsoChpDefault
{font-size:10.0pt;}
@page Section1
{size:8.5in 11.0in;}
.ExternalClass div.ecxSection1
{page:Section1;}
</style>





<div class="ecxSection1">

<p class="ecxMsoNormal" style="text-autospace:none"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">This was our last batch</span></p>

<p class="ecxMsoNormal" align="center" style="text-align:center;text-autospace:none"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<p class="ecxMsoNormal" align="center" style="text-align:center;text-autospace:none"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<p class="ecxMsoNormal" align="center" style="text-align:center;text-autospace:none"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<p class="ecxMsoNormal" style="text-autospace:none"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; </span><b><span style="font-size:17.5pt;font-family:'TimesNewRoman,Bold','serif'">Labeling For
Grid-tie Solar Electric System</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:11.5pt;font-family:'TimesNewRoman,Bold','serif'">Great Solar Works, Inc., 970-626-5253</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:11.5pt;font-family:'TimesNewRoman,Bold','serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:11.5pt;font-family:'TimesNewRoman,Bold','serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
KNOPP SIGNS&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; </span></b><b><span style="font-size:17.5pt;font-family:'TimesNewRoman,Bold','serif'"></span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:11.5pt;font-family:'TimesNewRoman,Bold','serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Qty  2, Color
red</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">INTERACTIVE SYSTEM
POINT OF INTERCONNECTION</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Enphase
Micro-Inverters [1] per module [17] Total</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">PHOTOVOLTAIC SYSTEM
SOURCE</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; PV
System Total
Watts&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 3.910
&nbsp; KW</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Maximum
AC Output Operating Current  &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 13.6
&nbsp;&nbsp;&nbsp; Amps</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; AC
Operating Voltage&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 240
&nbsp;&nbsp;&nbsp;&nbsp; Volts&nbsp; </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">For information and
service contact: </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Great Solar Works, Inc.,
970-626-5253</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Qty  1, Color
red</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">PHOTOVOLTAIC SYSTEM
SOURCE</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; PV
System Total
Watts&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 3.910
&nbsp; KW</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Maximum
AC Output Operating Current  &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 13.6
&nbsp;&nbsp;&nbsp; Amps</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; AC
Operating Voltage&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 240
&nbsp;&nbsp;&nbsp;&nbsp; Volts&nbsp; </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">For information and
service contact: </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Great Solar Works,
Inc., 970-626-5253</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Qty  1, Color
red</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:14.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:14.0pt;font-family:'Arial','sans-serif'">PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">WARNING - ELECTRIC
SHOCK HAZARD - DONOT TOUCH TERMINALS.</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">TERMINALS ON BOTH THE
LINE AND LOAD SIDES MAY BE ENERGIZED</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">IN THE OPEN POSITION.
IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED CONDUCTORS MAY BE
ENERGIZED AND UNGROUNDED</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">For information and
service contact: </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Great Solar Works,
Inc., 970-626-5253</span></b></p>

<p class="ecxMsoNormal" style="text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-family:'Arial','sans-serif'">Qty -1, Color Yellow</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:20.0pt;font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:20.0pt;font-family:'Arial','sans-serif'">PHOTOVOLTAIC SYSTEM
CONNECTED</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">THE AC PV DISCONNECT
IS LOCATED </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-size:11.0pt;font-family:'Arial','sans-serif'">Next to Meter on
South Wall </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-family:'Arial','sans-serif'">For information and service contact: </span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-family:'Arial','sans-serif'">Great Solar Works, Inc., 970-626-5253</span></b></p>

<p class="ecxMsoNormal" style="margin-left:.25in;text-autospace:none"><b><span style="font-family:'Arial','sans-serif'">&nbsp;</span></b></p>

<p class="ecxMsoNormal"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<p class="ecxMsoNormal"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<div>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">Thanks,&nbsp;
Dana Orzel</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">Great
Solar Works, Inc</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">E -
dana@solarwork.com</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">V -
970.626.5253</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">F -
970.626.4140</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">C -
970.209.4076</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">web
- www.solarwork.com</span></p>

<p class="ecxMsoNormal"><span style="font-family:'Century Gothic','sans-serif'">Responsible
Technologies for Responsible People since 1988"</span><span style="font-size:11.0pt;font-family:'Calibri','sans-serif'"></span></p>

</div>

<p class="ecxMsoNormal"><span style="font-size:14.0pt;font-family:'Century Gothic','sans-serif'">&nbsp;</span></p>

</div></div>

</div>


                                          <br /><hr />30 days of prizes: Hotmail makes your day easier! <a href='http://go.microsoft.com/?linkid=9729704' target='_new'>Enter now</a></body>
</html>