<font size=3>Kurt<br><br>
Fascinating story and valuable information.&nbsp; This is the kind of
real world experience we need to draw on.&nbsp; Reality can change
quickly under extreme conditions and one's education is not complete
without this understanding.<br><br>
Thanks for this post.<br><br>
William Miller<br><br>
PS:&nbsp; You are fortunate your client had a proper fire suppression
system.&nbsp; I doubt many of us can count on that to minimize
damage.<br><br>
Wm<br><br>
<br><br>
At 03:13 PM 5/16/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Voltage is not the issue here, it
is current, and battery fault currents can be staggering - far more than
one would ever encounter in a typical AC system fed from a distribution
transformer.&nbsp; I have seen a 200A Class T fail to act on an 48V
inverter fault which resulted in welding the metal tabs of the fuse
holder (which had been greased with copper-laden Penetrox E) to their
sockets.&nbsp; That indicates a fault current well north of 200,000 amps,
quite possibly sseveral times that.&nbsp;&nbsp; A fire ensued, which
triggered the gas protection system and fortunately resulted in almost no
peripheral damage.&nbsp; It did cost about $10k to recharge and recertify
the Inergen system.&nbsp; The inverter manufacturer was quite cagey on
warranty replacement until they saw the photos - at which point a
replacement miraculously arrived by overnight air.<br><br>