<html><body><span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>We went over this stuff in class last year.. I'm hoping some if it stuck... seems to me you're on table 450.3(B) of the NEC.. if you choose to&nbsp; protect the primary only, you're restricted to 125% of primary FLA. IF you choose to protect both primary and secondary, you can size to 250% of the primary, (For inrush), and 125% of the secondary.. (and you're allowed the next size larger fuse). Hope I'm not getting too far out in the rhubarb here, but I'm thinking you may be able to do a line side tap to a SE rated knife switch fused with a slow blow fuse... maybe? db<br></div><div><br></div><div><br>Dan Brown<br>President<br>Foxfire Energy Corp.<br>Renewable Energy Systems<br>(802)-483-2564<br>www.Foxfire-Energy.com<br>NABCEP #092907-44<br><br></div>
<blockquote id="replyBlockquote" webmail="1" style="border-left: 2px solid blue; margin-left: 8px; padding-left: 8px; font-size: 10pt; color: black; font-family: verdana;">
<div id="wmQuoteWrapper">
-------- Original Message --------<br>
Subject: Re: [RE-wrenches] Transformer inrush<br>
From: Richard.L.Ratico@valley.net (Richard L Ratico)<br>
Date: Thu, May 13, 2010 8:01 am<br>
To: re-wrenches@lists.re-wrenches.org<br>
<br>
Sorry for the additional post here, but it includes a typo correction:<br>
<br>
Bill,<br>
<br>
Not a lot of personal experience with this issue. The one time I had to deal<br>
with it, we were able to leave the circuit on, once we got it energized. <br>
As you know, the crux of the problem is the nature of the voltage relative to<br>
it's cycle when connection is attempted.<br>
<br>
An internet search resulted in this explanation that was very helpful. See:<br>
<br>
<a target="_blank" href="http://www.opamp-electronics.com/tutorials/inrush_current_2_09_12.htm">http://www.opamp-electronics.com/tutorials/inrush_current_2_09_12.htm</a><br>
<br>
As I understand it now, counterintuitively, you don't want to switch at the zero<br>
crossing. SS relays aren't my strong suit either, but if they connect at that<br>
moment.......<br>
<br>
Is your step up transformer actually designed by the manufacturer to be a step<br>
up unit, or are you using a step down unit in reverse? <br>
Again, according to information found in my search, not personal experience, the<br>
latter can contribute to higher than expected inrush.<br>
<br>
Dick Ratico<br>
<br>
<br>
--- You wrote:<br>
Thanks for the reply.  To clarify, we have tried his with one transformer <br>
and with two transformers.  Our success rate is lower powering one <br>
transformer.  My hunch is that the capacitance of the feeder is buffering...<br>
<br>
I wonder if I use a large solid state relay with zero crossing switching I <br>
might have better luck.<br>
<br>
<br>
William Miller<br>
<br>
<br>
At 06:23 PM 5/12/2010, Richard L Ratico wrote:<br>
&gt;Bill,<br>
&gt;Your branch circuit breaker is pretty small.<br>
&gt;Are you energizing both transformers simultaneously? If so, it might help to<br>
&gt;energize them individually.<br>
&gt;<br>
&gt;The branch breaker can be up to 250% of the step up transformer's primary<br>
&gt;rating. 10kVA/240V=41A.<br>
&gt;41A x 2.5=100A. (round numbers). To do this you would also need overcurrent<br>
&gt;protection on the transformer secondary.<br>
&gt;<br>
&gt;Of course, you've already got the 100A main tripping. That's why I asked if<br>
&gt;you're<br>
&gt;energizing them simultaneously.<br>
&gt;<br>
&gt;Transformer inrush can be a real problem.<br>
&gt;<br>
&gt;Hope this helps.<br>
&gt;<br>
&gt;Dick Ratico<br>
&gt;Solarwind Electric<br>
&gt;<br>
&gt;--- You wrote:<br>
&gt;Friends:<br>
&gt;<br>
&gt;I have on off-grid client that is trying to eliminate winter generator run<br>
&gt;time.  He has a rental on another corner of the property that has grid<br>
&gt;power.  When it was installed, he put in an extra meter, hoping to use it<br>
&gt;to run a utility back up feeder to charge batteries.<br>
&gt;<br>
&gt;We are now installing this feeder.  We purchased two 10KVA 240/600 volt<br>
&gt;transformers to bump the voltage to 600 and then back down to 120/240.<br>
&gt;<br>
&gt;Here's the problem:  when we energize the circuit breaker that feeds the<br>
&gt;transformer, the circuit breaker AND the main breaker trip.  The<br>
&gt;transformer is 10KVA, the main is 100 amps and the branch breaker is<br>
&gt;60A.  The breakers hold sometimes but trip other times.  This is obviously<br>
&gt;an inrush problem.  How do I correct this problem?<br>
&gt;<br>
&gt;Thanks in advance,<br>
--- end of quote ---<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Options &amp; settings:<br>
<a target="_blank" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a target="_blank" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a target="_blank" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a target="_blank" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
<br>

</div>
</blockquote></span></body></html>