<font size=3>Friend:<br><br>
Thanks for the responses.&nbsp; They have all been valid on offered good
options.&nbsp; There is one possible solution that will be easier to
implement and is worth a brief description here:<br><br>
Breakers have an AIC (Ampere Interrupting Capacity).&nbsp; This is a
quantification of how much fault current a breaker can handle before it
explodes (in lay terms).&nbsp; Residential AC power distribution drops
have a finite ampacity under short circuit capability.&nbsp; Sure, you
drop a wrench across a bus expect a lot of amps to flow until your main
opens.&nbsp; A higher amperage commercial service can deliver more
instantaneous amps, so a breaker with a higher AIC is required in
commercial applications.&nbsp; Typical values are 10,000, 22,000 and
65,000.&nbsp; The lower values are found on garden variety
breakers.<br><br>
I have learned that the higher AIC breakers also have a higher
&quot;instantaneous trip&quot; value.&nbsp; A Siemens 2 pole 100 amp
breaker with a10,000 AIC rating has a 600-900 amps instantaneous
rating.&nbsp; The same breaker with a 22,000 AIC rating has a rating of
rating of 1,000 -1,2000 instantaneous amps.<br><br>
I am thinking that the higher instantaneous rating my prevent nuisance
trips.&nbsp; My supplier has asked Siemens to comment but we receive a
very non-committal answer.&nbsp; My supplier has offered to sell me
breakers with the higher AIC and accept them back if they don't solve the
problem.&nbsp; That is the direction and I will report back.<br><br>
Thanks again.&nbsp; I hope this exchange was beneficial for many of you
and prevents some of you from repeating my mistakes.<br><br>