Friends:<br><br>
I have on off-grid client that is trying to eliminate winter generator
run time.&nbsp; He has a rental on another corner of the property that
has grid power.&nbsp; When it was installed, he put in an extra meter,
hoping to use it to run a utility back up feeder to charge
batteries.<br><br>
We are now installing this feeder.&nbsp; We purchased two 10KVA 240/600
volt transformers to bump the voltage to 600 and then back down to
120/240.<br><br>
Here's the problem:&nbsp; when we energize the circuit breaker that feeds
the transformer, the circuit breaker AND the main breaker trip.&nbsp; The
transformer is 10KVA, the main is 100 amps and the branch breaker is
60A.&nbsp; The breakers hold sometimes but trip other times.&nbsp; This
is obviously an inrush problem.&nbsp; How do I correct this
problem?<br><br>
Thanks in advance,<br><br>
William Miller<br><br>