<html>
<body>
<font size=3>Dick:<br><br>
Thanks for the reply.&nbsp; To clarify, we have tried his with one
transformer and with two transformers.&nbsp; Our success rate is lower
powering one transformer.&nbsp; My hunch is that the capacitance of the
feeder is buffering...<br><br>
I wonder if I use a large solid state relay with zero crossing switching
I might have better luck.<br><br>
<br>
William Miller<br><br>
<br>
At 06:23 PM 5/12/2010, Richard L Ratico wrote:<br>
<blockquote type=cite class=cite cite>Bill,<br>
Your branch circuit breaker is pretty small.<br>
Are you energizing both transformers simultaneously? If so, it might help
to<br>
energize them individually.<br><br>
The branch breaker can be up to 250% of the step up transformer's
primary<br>
rating. 10kVA/240V=41A.<br>
41A x 2.5=100A. (round numbers). To do this you would also need
overcurrent<br>
protection on the transformer secondary. <br><br>
Of course, you've already got the 100A main tripping. That's why I asked
if<br>
you're<br>
energizing them simultaneously. <br><br>
Transformer inrush can be a real problem. <br><br>
Hope this helps.<br><br>
Dick Ratico<br>
Solarwind Electric <br><br>
--- You wrote:<br>
Friends:<br><br>
I have on off-grid client that is trying to eliminate winter generator
run <br>
time.&nbsp; He has a rental on another corner of the property that has
grid <br>
power.&nbsp; When it was installed, he put in an extra meter, hoping to
use it <br>
to run a utility back up feeder to charge batteries.<br><br>
We are now installing this feeder.&nbsp; We purchased two 10KVA 240/600
volt <br>
transformers to bump the voltage to 600 and then back down to
120/240.<br><br>
Here's the problem:&nbsp; when we energize the circuit breaker that feeds
the <br>
transformer, the circuit breaker AND the main breaker trip.&nbsp; The
<br>
transformer is 10KVA, the main is 100 amps and the branch breaker is
<br>
60A.&nbsp; The breakers hold sometimes but trip other times.&nbsp; This
is obviously <br>
an inrush problem.&nbsp; How do I correct this problem?<br><br>
Thanks in advance,</font></blockquote></body>
</html>