Wrenches,<div><br></div><div>We are working through submittal steps for a 75 kW ground mounted array. The array is split into 8 subarrays. There is a combiner or junction box at each subarray, with a ground rod spec&#39;d at each subarray, underneath the &quot;box station&quot;, with a bare stranded #6 from an equipment grounding bus to the rod, and equipment grounding conductors through conduit between a ground bus in each box. 15A fuses in combiners, and 100A fuses at inverter.</div>
<div><br></div><div>The engineer we&#39;re working with to stamp the plans wants to see bare, tinned, solid copper anywhere this equipment ground is in the elements, and wants to see #2 (!) bare, tinned, solid copper cadwelded and direct-buried between all 8 rods and back to the existing AC grounding electrode system. He says this is the standard (from telecom, I&#39;m afraid) to ensure that all the rods are at the same potential. No Code reference, and I don&#39;t see anything in article 250 along these lines. Hard to convince him that #6, untinned, across the board is adequate.</div>
<div><br></div><div>In the end, we&#39;ll probably go ahead and do it because it is relatively low cost and we want a good relationship here, but I&#39;m wondering if anybody else out there is using bare tinned copper in this type of application, and I&#39;d like more info on this to make a better argument next time.</div>
<div><br></div><div>Phil</div><div><br></div><div>Phil Schneider<br>Creative Energies<br><br>
</div>