<font face="Arial">Esteemed Wrenches,<br>
<br>
I'm in the process of bidding a small government job.&nbsp; They're
requiring the following tests.&nbsp; I was wondering if any of you have
ever run across this before and if so how you went about it. <br>
<br>
<i>- Inspect&nbsp;&nbsp; inverters&nbsp;&nbsp; according&nbsp;&nbsp; to&nbsp;&nbsp; requirements&nbsp;&nbsp; in&nbsp;&nbsp; NETA
Acceptance&nbsp;&nbsp; Testing <br>
Specifications. <br>
<br>
- Test&nbsp; the&nbsp; PV&nbsp; system&nbsp; under&nbsp; prime&nbsp; solar&nbsp; design&nbsp; conditions&nbsp; to&nbsp;
validate&nbsp; system <br>
power&nbsp; performance&nbsp; rating.&nbsp;&nbsp;&nbsp; Use&nbsp; instruments&nbsp; calibrated&nbsp; within&nbsp;
the&nbsp; previous&nbsp; six <br>
months according to NIST standards.&nbsp;&nbsp; </i>(not easy since the site
they've chosen will shade some of the array all the time.&nbsp; I should be
able to just explain this to them)<br>
<i><br>
- Simulate&nbsp; malfunctions,&nbsp; including&nbsp; ground&nbsp; faults,&nbsp; to&nbsp; verify&nbsp;
protective&nbsp; device <br>
operation.&nbsp;&nbsp; </i>(I would create a GF and then replace the fuse for
this test)<br>
<i><br>
- Test&nbsp; anti-islanding&nbsp; shutdown&nbsp; function&nbsp; due&nbsp; to&nbsp; normal&nbsp; utility&nbsp;
source&nbsp; failure, <br>
time delay and automatic restart after utility power restoration.&nbsp; </i>(this
is an easy one)<br>
<i><br>
- Test&nbsp; and&nbsp; record&nbsp; the&nbsp; total&nbsp; harmonic&nbsp; distortion&nbsp; (THD)&nbsp; content&nbsp;
of&nbsp; output <br>
current at 25, 50, and 100 percent of system rating.&nbsp; Comply with IEEE
519 <br>
at MDP point of connection. <br>
<br>
- Test&nbsp; and&nbsp; record&nbsp; the&nbsp; real&nbsp; power&nbsp; output&nbsp; for&nbsp; each&nbsp; inverter,&nbsp;
and&nbsp; total&nbsp; power <br>
delivered at the grid tie connection, for a 24 hour period.&nbsp; The
continuous <br>
power&nbsp;&nbsp; output&nbsp;&nbsp; during&nbsp;&nbsp; prime&nbsp;&nbsp; solar&nbsp;&nbsp; conditions&nbsp;&nbsp; shall&nbsp;&nbsp; meet&nbsp;&nbsp;
or&nbsp;&nbsp; exceed <br>
performance requirement under part I of this specification. <br>
<br>
- For&nbsp; each&nbsp; inverter,&nbsp; record&nbsp; DC&nbsp; input&nbsp; voltage&nbsp; for&nbsp; 24&nbsp; hours,&nbsp;
to&nbsp; demonstrate <br>
affects of maximum power point tracking (MPPT), voltage regulation
within <br>
inverter&nbsp; rated&nbsp; limits,&nbsp; and&nbsp; affect&nbsp; of&nbsp; partial&nbsp; shading&nbsp; on&nbsp; solar&nbsp;
modules.&nbsp; <br>
Simulate&nbsp; partial&nbsp; shading&nbsp; by&nbsp; covering&nbsp; 50%&nbsp; of&nbsp; modules&nbsp; during&nbsp;
prime&nbsp; solar <br>
conditions. <br>
<br>
- Record&nbsp; of&nbsp; Tests&nbsp; and&nbsp; Inspections:&nbsp;&nbsp;&nbsp; Prepare&nbsp; and&nbsp; submit&nbsp;
documentation&nbsp; of&nbsp; tests&nbsp; and <br>
inspections,&nbsp; including&nbsp; references&nbsp; to&nbsp; manufacturers'&nbsp; written&nbsp;
instructions&nbsp; and&nbsp; other&nbsp; test <br>
and inspection criteria.&nbsp; Include results of tests, inspections, and
retests. <br>
<br>
</i><br>
Any advice would be gratefully accepted and appreciated!<br>
<br>
Best,<br>
<br>
Greg Egan<br>
<br>
NABCEP Certified PV Installer<br>
Remote Power Inc.<br>
Fairbanks, AK</font>