<font size=3>Friends:<br><br>
Over the years we used all lengths and diameters of lags.&nbsp; We do not
use any of these lags anymore, ever since we discovered the Simpson
1/4&quot;X3&quot; hot dip galvanized strong drive lags.&nbsp; They
require no pilot hole, drive easily with an impact driver and the
inspectors and plan checkers seem to like hearing the Simpson brand name
used on the plans.&nbsp; The 1/4&quot; diameter is less likely to split a
2 by truss.<br><br>
Finding the center of a truss is critical and pilot holes are a necessary
evil.&nbsp; We issue each employee a specific color of lumber crayon with
instructions to circle every pilot hole.&nbsp; They then &quot;own&quot;
that pilot hole and are responsible for sealing it.&nbsp; Hopefully, each
pilot hole ends up under a foot anyway.<br><br>
We use landscape flags to probe pilot holes.&nbsp; The thin wire will
prove if you have hit a truss.&nbsp; If you miss the truss, bend a slight
angle on the wire and rotate it until the end strikes the side of the
truss.&nbsp; Extract the wire and hold it in the same orientation as when
you touched the side of the truss and it will tell you accurately where
the edge is.&nbsp; If someone needs to crawl the attic to put in
blocking, wind the flag tightly around the wire and insert it in the
pilot hole.&nbsp; It will unfurl and mark the spot so it can easily be
seen even in the dustiest attic.<br><br>
William Miller<br><br>
Does anyone out there want to buy a bucket of various size 
lags?<br><br>
WM<br><br>
<br><br>
<br><br>
<br>
At 12:28 PM 4/27/2010, you wrote:<br>
<blockquote type=cite class=cite cite>Hi Drake and all,<br><br>
We have had both engineers and inspectors question the use of a 3/8&quot;
4&quot; lag in a 2x4 top chord and I think rightfully so.&nbsp; When we
have a chance to spec new construction we have the architect replace the
2x4 top&nbsp; chord with a 2x6.<br><br>
And when we have to go into 2x4's we either shorten our lag to a
5/16&quot; 3.5&quot; or even 3&quot; (if we can get away with it on the
uplift calcs) so we stay in the top half of the wood fibers on the
truss.&nbsp;&nbsp; We have also sistered or blocked 2x4s when there was
concern.<br><br>
But like Bruce said - I cannot imagine there ever being a problem with a
2x6 with a 4 &quot; lag (only 3.5&quot; of which goes into the wood)
unless you were using 1/2&quot; lags!<br><br>
The real issue is in installation.&nbsp; Installing a lag so that it
glances the side and splits the rafter or hitting a knot and not backing
off could cause problems.&nbsp; So we are really careful in installation
to make sure we are right on the center of the truss - we drill tiny
probes everytime - that's where the real issue is - once engineering is
happy of course.<br><br>
Hope that helps!<br><br>
Jeff Clearwater<br>