<div>Hi Mark,</div>
<div><br></div>
<div>Yes I've done several grid-tie hydro systems.&nbsp; As Dave says
Derik is&nbsp; your man for components.&nbsp; I've also worked with
SMA to tweak the settings on the SB to be a WB (&quot;water
boy&quot;).&nbsp; Actually no tweaks are absolutely necessary.&nbsp;
But if you shorten the reset time it helps when the hydro goes down
and you are trying to test it to bring it back up.&nbsp; Derik is
aware of these tweak refinements but it will work without any
tweaks.</div>
<div><br></div>
<div>We have been running 2&nbsp; 2500 watt induction generators into
two 2500 &quot;Water Boys&quot;&nbsp; at one site now since the spring
of '06 - 24 hours/day with no inverter failures.&nbsp; We throttled
the water down so that the each inverter see a continuous 2200 watts.&nbsp;
We don't dare to go higher as they run pretty hot at that.&nbsp; 4400
watts continuous is 3168 KWHs/Month= 38,000 KWHrs/yr!&nbsp; Runs the
whole ranch - Install cost was around $20,000.&nbsp; Can send pics if
you'd like.</div>
<div><br></div>
<div>Make sure you use redundant load dumps!</div>
<div><br></div>
<div>Best,</div>
<div><br></div>
<div>Jeff Clearwater</div>
<div>Village Power Design</div>
<div><br></div>
<div><br></div>
<div><br></div>
<div><br></div>
<div><br></div>
<div><br></div>
<blockquote type="cite" cite>Derik at HI Power hydro has done several
of these with grid tie DC voltage with diversion.<br>
You can reach him at <a
href="mailto:derik@asis.com">derik@asis.com</a><br>
<a
href="http://www.hipowerhydro.com/">http://www.hipowerhydro.com/</a><br
>
cheers,<br>
David<br>
</blockquote>
<blockquote type="cite" cite>David Katz<br>
</blockquote>
<blockquote type="cite" cite>David Katz<br>
</blockquote>
<blockquote type="cite" cite>Chief Technical Officer<br>
</blockquote>
<blockquote type="cite" cite>AEE Solar<br>
</blockquote>
<blockquote type="cite" cite>1155 Redway Drive<br>
</blockquote>
<blockquote type="cite" cite>P.O. Box 339<br>
</blockquote>
<blockquote type="cite" cite>Redway, CA&nbsp; 95560<br>
</blockquote>
<blockquote type="cite" cite>Tel (707) 825-1200<br>
</blockquote>
<blockquote type="cite" cite>Fax (707) 825-1202<br>
</blockquote>
<blockquote type="cite" cite><a
href="mailto:david@aeesolar.com">dkatz@aeesolar.com</a><br>
</blockquote>
<blockquote type="cite" cite><a
href="http://www.aeesolar.com/">www.aeesolar.com</a><br>
</blockquote>
<blockquote type="cite" cite>&nbsp;<br>
</blockquote>
<blockquote type="cite" cite>DISCLAIMER:<br>
This communication, along with any documents, files or attachments, is
intended for the use of only the addressee and contains privileged and
confidential information.&nbsp;If you are not the intended recipient,
you are hereby notified that any dissemination, distribution or
copying of any information contained in or attached to this
communication is strictly prohibited.&nbsp; If you have received this
message in error, please notify the sender immediately by e-mail reply
and destroy the original communication and its attachments without
reading, printing or saving in any manner.<br>
</blockquote>
<blockquote type="cite" cite>&nbsp;<br>
</blockquote>
<blockquote type="cite" cite><br>
<br>
Mark Dickson wrote:<br>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">Hello Wrenches,</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">Got one for you. . .</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">We have a customer that has great potential for a
micro-hydro system and already has the grid on his property.&nbsp; The
obvious way to tie the turbine unit in would be to go back through
batteries and a GVFX or XW.&nbsp; In trying to eliminate the batteries
and the inefficiencies I want to look at using a battery-less grid-tie
inverter.&nbsp; I am assuming that I could use a small inverter such
as the PVP 1100 and high-voltage Stream Engine.&nbsp; The problem I am
trying to work around is how to divert the ~240DC output of the
turbine, if and when the grid goes down.&nbsp; Would this be as simple
a placing a relay on the AC side of the inverter and having it switch
on/off a large diversion load?</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">For the diversion load I was thinking I could just
series up a set of water heater elements to get to the necessary
voltage.</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">&nbsp;</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">Has anybody accomplished this before?&nbsp; Jay?&nbsp;
Are there any other elegant solutions for this?</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">&nbsp;</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">Has anybody successfully used a WindyBoy with
hydro?</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1"
color="#000080">&nbsp;</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Comic Sans MS" size="-1"
color="#000080">Best regards,</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Comic Sans MS" size="-1"
color="#000080">&nbsp;</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Comic Sans MS" size="-1"
color="#000080">Mark Dickson,</font><br>
</blockquote>
<blockquote type="cite" cite><font size="-1" color="#000080">NABCEP
Certified Solar PV Installer </font><br>
</blockquote>
<blockquote type="cite" cite><font face="Comic Sans MS" size="-1"
color="#000080">Oasis Montana Inc.</font><br>
</blockquote>
<blockquote type="cite" cite><font face="Calibri"
size="-1">&nbsp;</font><br>
</blockquote>
<blockquote type="cite" cite><tt><br></tt></blockquote>
<blockquote type="cite" cite>
<hr size="4" width="90%"></blockquote>
<blockquote type="cite" cite><tt><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address:</tt> <a
href="mailto:RE-wrenches@lists.re-wrenches.org"><tt
>RE-wrenches@lists.re-wrenches.org</tt></a><tt><br>
<br>
Options &amp; settings:<br>
</tt><a
href=
"http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
><tt
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</tt
></a><tt><br>
<br>
List-Archive:</tt> <a
href=
"http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"><tt
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</tt
></a><tt><br>
<br>
List rules &amp; etiquette:<br>
</tt><a
href="http://www.re-wrenches.org/etiquette.htm"><tt
>www.re-wrenches.org/etiquette.htm</tt></a><tt><br>
<br>
Check out participant bios:<br>
</tt><a
href="http://www.members.re-wrenches.org"><tt
>www.members.re-wrenches.org</tt></a><tt><br>
<br>
&nbsp;</tt><br>
</blockquote>
</blockquote>
<blockquote type="cite" cite><br>
_______________________________________________<br>
List sponsored by Home Power magazine</blockquote>
<blockquote type="cite" cite><br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Options &amp; settings:<br>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br
>
<br>
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br>
<br>
List rules &amp; etiquette:<br>
www.re-wrenches.org/etiquette.htm<br>
<br>
Check out participant bios:<br>
www.members.re-wrenches.org</blockquote>
<div><br></div>
<div><br></div>
<x-sigsep><pre>-- 
</pre></x-sigsep>
<div>~~~~~~~~~~~~~~~~~~~<br>
Jeff Clearwater<br>
Senior Design Engineer<br>
NABCEP (tm) Certified Solar PV Installer<br>
http://www.nabcep.org/<br>
Village Power Design<br>
Solar Design Consultation for the Commercial Sector<br>
http://www.villagepower.com<br>
gosolar@villagepower.com<br>