<font size=3>Eirka:<br><br>
Although the Imp is your normal operating condition, you need to design
wire size for an abnormal occurrence (short circuit or other
fault).&nbsp; You do not want the wire to burst in to flame after an
unplanned short circuit, do you?&nbsp; Remember, you may have combiner
fuses, but you have no overcurrent protection to open circuits when a
fault occurs in a PV feeder.&nbsp; See
<a href="http://millersolar.com/practices/Safety/safety_data.html" eudora="autourl">http://millersolar.com/practices/Safety/safety_data.html</a>
, click on Target PV fire.<br><br>
Correct wire sizing is not a waste of money.&nbsp; Loosing output power due to wire heating is a waste of money.&nbsp; Burning down the house is a waste of money.<br><br>
William Miller<br><br>
<br><br>
At 06:27 AM 4/2/2010, you wrote:<br>
</font><blockquote type=cite class=cite cite><font face="Century Gothic, Avant Garde" size=2>To my understanding the 156% on PV source and output circuits is related to the ability of PV to deliver more than rated and be continuous.<br>
Therefore, the wire has to be able to carry this current, so now the temperature and fill corrections are applied to find the wire capable of the 156%.<br>
&nbsp;<br>
I am in a debate where the question is why correct for temp and fill on 156% of ISC and spend all that extra money when the normal operating is at Imp. Or why correct the 156% but why not correct the Isc or Imp.<br>
&nbsp;<br>
I am going to stick to the fact that the circuit has to carry the 156% under all conditions<br>
Thoughts? <br>
&nbsp;<br>
Erika</font></blockquote></body>