<div>All,</div>
<div></div>
<div>If the grid-tie inverter is operating under UL1741 (and therefore IEEE1547), then the inverter has to cease output within 1 second of the voltage going over 10% of the base voltage. So in the case where the generator is outputting and theload is less than the inverter output, the voltage will rise and the inverter will cease to ouput. The voltage will then drop, the inverter will reconnect, and the cycle will repeat itself. That assumes the generator's waveform is clean enough for the inverter to connect to in the first place. James Worden from Solectria Renewables covered this briefly in a SolarPro article: <a href="http://solarprofessional.com/article/?file=SP2_5_pg16_QandA_2">http://solarprofessional.com/article/?file=SP2_5_pg16_QandA_2</a>.</div>
<div></div>
<div>- Mike</div>
<div>--<br>Michael Kelly<br>Project Manager / Project Engineer<br>NABCEP Certified Solar PV Installer <br><br>SolarFlair Energy, Inc.<br>11 Mayhew Street<br>Framingham, MA 01702<br>Direct Mobile: 617-899-9840<br>Main Phone: 508-293-4293<br>
Main Fax: 508-293-4003<br><a href="mailto:mike@solarflair.com">mike@solarflair.com</a><br><br><br></div>
<div class="gmail_quote">On Tue, Mar 2, 2010 at 9:29 AM, Drake Chamberlin <span dir="ltr"><<a href="mailto:drake.chamberlin@redwoodalliance.org">drake.chamberlin@redwoodalliance.org</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div><font color="#0000ff">I was recently told by SMA that in the event that the inverters did connect to generator output, and the load was less than the inverter output, that the voltage would rise and the inverters would fall off line. A year or so before I'd been told by another SMA representative that generator circuit boards had been fried by inverter backfeed. <br>