<p class="MsoNormal"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">Allen,<br>
<br>
You're correct about current dividing between two or more paralleled sets of
batteries, and your resulting ability to use reduced conductor size in each
set.&nbsp; As long as you ensure the conductor ampacity for each set of
batteries is sized according to the current they will conduct .. you're good to
go.<br>
<br>
There are generally three primary points to consider:<br>
<br>
1) Total current flowing in each circuit;<br>
2) The ampacity of the conductors involved, and;<br>
3) Voltage drop.<br>
<br>
This then raises a question.&nbsp; Do you size the battery conductors to meet
the maximum continuous current flow .. or the peak surge current?<br>
<br>
The answer is, you can do either one, depending on your goal - and that of your
customer.&nbsp; Conductors of appropriate gauge for maximum continuous current
flow will handle the typical 2X surge current that [for example] would be
required to start a submersible well pump, and will do so without
overheating.&nbsp; Surge currents typically exist for periods of time ranging from much
less than a second to 2 or 3 seconds at most.&nbsp; After that, if the surge
current still exists, overcurrent devices open or inverters shut down --
whichever happens first.<br>
<br>
If you size for maximum continuous current flow .. you economize on conductor
costs.&nbsp; Size for surge current, and your customer pays more, but their
system experiences lower voltage drop across the conductors and connections during the
surge.&nbsp; It's all a matter of which aspect of the system design is more
important to your customer.&nbsp; As we know, sometimes a few tenths of a
volt one way or the other (at the inverter) can make the difference between
starting a high-surge load -- or not.<br>
<br>
As a related comment, when I'm designing and building battery systems that
require large conductors (for instance 4/0), I'll use paralleled pairs of 1/0
from one battery (or cell) to the next.&nbsp; Two paralleled 1/0 are equivalent to
one 4/0, but there are advantages to the paralleled conductors.&nbsp; I place one
cable lug on each side of a battery post, then install and torque the hardware.&nbsp; This doubles the effective
total surface area of the lugs in contact with the battery posts, reducing the
high-current voltage drop at each of these points in the system.&nbsp; This approach increases the total
conductor surface area in contact with the cable lugs, and with a lug on either
side of the battery post, also provides something stronger than a standard flat washer to
torque against.&nbsp; Admittedly a more expensive way to go, but I feel it's
worth it.<br>
<br>
<br>
Dan<br>
<br>
<br>
--- On <b>Fri, 2/19/10, Allan Sindelar <i>&lt;allan@positiveenergysolar.com&gt;</i></b>
wrote:<o:p></o:p></span></p>

<p class="MsoNormal" style="margin-bottom: 12pt;"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;"><br>
From: Allan Sindelar &lt;allan@positiveenergysolar.com&gt;<br>
Subject: Re: [RE-wrenches] single string of batts: must the interconnects be
inverter size cables?<br>
To: "RE-wrenches" &lt;re-wrenches@lists.re-wrenches.org&gt;<br>
Date: Friday, February 19, 2010, 11:03 PM<o:p></o:p></span></p>

<p class="MsoNormal" style="margin-bottom: 12pt;"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">Phil,<br>
Given the scenario that Mick presented, your advice is sound, and I'd do as you
suggest. But by changing the scenario just a bit, it brings up a separate but
related issue. <br>
<br>
Mick's scenario describes two 12V batteries in series, or a single string. In
that case all current flows through the one string, so a series interconnect
would need to be sized equal to the battery cables, in this case 4/0. But if
there were two (or more) parallel strings, would the same size requirement
apply? That is, if a battery bank had two strings, in theory each would carry
180 max amps (your example, 8,000/22, shared by 2 strings), which is within the
ampacity of 2/0 interconnects. In reality, this only applies if current is
equally spread among strings. Is it? <br>
<br>
It seems to me that a properly wired and torqued set will split current paths
equally until a cell fails, either prematurely or when the set approaches end
of life. If there are three strings, then failure of one cell/string in this
example would still not exceed ampacity on the remaining 2/0 strings.<br>
<br>
As with many issues, the goal is to find a balance between safety and
performance versus cost and worst-case accommodation. I will always use 4/0
with one cell string and a 250A breaker, but I have never seen a real-world
problem using 2/0 interconnects, both series and parallel, with 2 or more
strings. Phil, what do you say? Others?<o:p></o:p></span></p>

<p class="MsoNormal" style=""><b><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">Allan Sindelar</span></b><span style="font-family: &quot;Times New Roman&quot;;"><br>
Allan@positiveenergysolar.com<br>
NABCEP Certified Photovoltaic Installer<br>
EE98J Journeyman Electrician<br>
<b>Positive Energy, Inc.</b><br>
3201 Calle Marie<br>
Santa Fe, New Mexico 87507<br>
<b>505 424-1112</b><br>
<a href="http://www.positiveenergysolar.com/" target="_blank">www.positiveenergysolar.com</a></span><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;"><br>
<br>
Phil Undercuffler wrote: <o:p></o:p></span></p>

<p class="MsoNormal" style="margin-bottom: 12pt;"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">The interconnects are part of the circuit.&nbsp;
Typical flexible cables used with batteries are THW rated (75C column), so in
free air 2/0 interconnects would be good for 265 amps, before any temperature
derates.&nbsp; Therefore, you'd be safe from a NEC point of view.&nbsp;
However, if the inverter manufacturer has recommended 4/0 cables, then that
recommendation would apply to all cables in the circuit.&nbsp; Battery based
inverters are asked to surge many times their rated capacity -- a 24V 4kW
inverter surging to 2x capacity (pretty normal circumstances) is going to draw
over 360 amps (8,000 / 22), even if only for a short period of time.&nbsp; You
don't want your interconnects to be the weak link in the system, causing
shutdowns due to undervoltage unnecessarily.&nbsp; <br>
<br>
I'd use 4/0.<br>
<br clear="all">
Phil Undercuffler<br>
Conergy<br>
<br>
<br style="">
<!--[if !supportLineBreakNewLine]--><br style="">
<!--[endif]--><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">On
Fri, Feb 19, 2010 at 12:01 PM, Mick Abraham wrote:<o:p></o:p></span></p>

<p class="MsoNormal" style="margin-bottom: 12pt;"><span style="font-size: 12pt; font-family: &quot;Times New Roman&quot;;">Example: 12 two volt battery cells in one 24 volt
string. 4kW inverter/charger has 250 amp DC breaker size and 4/0 cables...as
the inverter folks would want.<br>
<br>
So...do the "cell to cell" interconnect cables have to also be 4/0?
In the example above, 2/0 interconnects would suffice from the standpoint of
basic safety...and even from the voltage drop standpoint...right?<br>
<br>
Inverter company people may be best qualified to answer this, but any replies
will be appreciated. While I'm at it: do the inverter folks request oversize
cables because they want more capacitance on the DC input...or what?<br>
<br>
Jolliness,<br>
<br clear="all">
Mick Abraham, Proprietor<br>