<div>At 09:34 -0800 19/1/10, Kent Osterberg wrote:</div>
<blockquote type="cite" cite><br>
The Peukert capacity equation gives a &quot;pretty good&quot; estimate
of the total amphours available at the present discharge current,
regardless of what the discharge current was in the past.</blockquote>
<div><br></div>
<div>In other words it tells you the 'capacity' at a particular load
current based on a fixed terminal voltage (end of discharge cut-off).&nbsp;
It does not tell you about all of the extra amphours you can still get
using a lower current and the same terminal voltage.</div>
<div><br></div>
<blockquote type="cite" cite>&nbsp;I certainly wouldn't want to treat
a set of batteries the way that Doerffel and Sharkh did.</blockquote>
<div><br></div>
<div>Nor me and it is a pity that the trials did not focus more on
partial discharge situations.&nbsp; But what's interesting is that
Peukert only works at constant discharge rates.</div>
<div><br></div>
<div>At 03:39 -0700 19/1/10, Warren Lauzon wrote:</div>
<blockquote type="cite" cite><br></blockquote>
<blockquote type="cite" cite><font face="Calibri" size="-1">Some of
the loss is in heat due to internal resistance, and that cannot be
recovered.</font></blockquote>
<div><br></div>
<div>Of course.&nbsp; But in this debate we are discussing amphours
and the effect of rapid discharge on the amphours that a battery can
deliver.&nbsp; I was concerned to find out about missing amphours and
to estimate how many are lost and where they went.&nbsp; According to
Peukert (as it is normally interpreted) you lose big chunks of the
amphours capacity by rapidly discharging the battery.&nbsp; According
to the Doerffel and Sharkh data, only 5-10% of the amphours are lost
in a high discharge use of the battery.&nbsp; This is way less than
Peukert's law would predict.</div>
<div><br></div>
<div>At 10:45 -0500 19/1/10, Drake Chamberlin wrote:</div>
<blockquote type="cite" cite>What I think I understand is that if a
battery is discharged completely at a high discharge rate, a
significant number of amp hours will be lost due to heat and
inefficiency, and Peukert's equation will approximate the loss.
</blockquote>
<div><br></div>
<div>Most of the heat is due to the voltage loss.&nbsp; Some of it may
be due to the amphours loss.&nbsp; But in the end Peukert only tells
us how many amphours you can get at a fixed discharge rate and based
on a chosen terminal voltage.&nbsp; It does not actually tell you how
much of the battery capacity is used nor how much is still available
under conditions of slower discharge.</div>
<div><br></div>
<div>Naive use of Peukert over-estimates the DOD caused by high
discharge currents.&nbsp; Peukert can be correctly used to predict how
many amphours you can get from a battery at a constant charge rate
before it reaches a certain terminal voltage.&nbsp; It does not tell
you the SOC of a battery.&nbsp; This last is a very hard thing to
ascertain.</div>