<div>Thanks, Kent,</div>
<div><br></div>
<div>It is clear then that high discharge rates have a big effect on
the voltage, but only&nbsp; a small effect on the actual battery
capacity.&nbsp; That was my instinct but it's good to have it
confirmed.&nbsp; And this will be important information for those who
use Peukert's Law 'naively' to conclude that a battery has
dramatically lower capacity when discharged at higher rates.&nbsp; (In
fact if it were true that capacity is reduced to this extent it would
also have very serious implications for battery efficiency.)</div>
<div><br></div>
<div>Battery voltage during discharge does depend heavily on discharge
rate, and hence it is hard to assign a voltage that will accurately
represent a 'good' end of discharge where the battery will not be
damaged/worn out/ sulphated. </div>
<div><br></div>
<div>I have worked with Australian inverters that use amphour
measurements to calculate the SOC as well as using voltage set-points
as a back up.&nbsp; This seems laudable on the face of it, but the
added complexity makes it very difficult to interpret why the
generator is still running.&nbsp; (Is it low voltage, low amphours,
high load, favourite time of day for generator, favourite time of
month for a boost charge, failure to synch, manual start, etc.....&nbsp;
) </div>
<div><br></div>
<div>It's not easy to get an accurate calibration for SOC based on
amphour logging, especially if the battery is wandering between 50%
and 80% SOC over a period.&nbsp; This is the most efficient zone of
operation, so it's not a bad state of affairs per se.&nbsp; While it
is good to get up to full charge periodically, this will involve a lot
of gassing and hence lost amphours/watthours in the system.&nbsp; I
prefer not to do this with fossil fuels unless it seems essential to
the health of the battery.</div>
<div><br></div>
<div>Anyway meantime I do have to assign genstart voltages for a
couple of systems that function automatically, and I will probably
continue to use values around 23.5 volts (11.7, 47 volts) for this
purpose.&nbsp; There's a bit of guesswork involved because of the
unknown current and temperature, but that's a value that has worked
well enough in the past.&nbsp; I am running a poll on my blog to see
what other people choose. http://scoraigwind.blogspot.com/&nbsp; It's
not a very well defined question, but so far the answers do peak at 47
volts so I am not alone in my choice.</div>
<div><br></div>
<div>Using a voltage rather than SOC for such purposes (user guidance,
genstart, etc) does have the advantage that it combines SOC and energy
use into one parameter.&nbsp; If the user is hitting the battery too
hard for the present conditions then the voltage will tend to hit the
chosen 'danger level' and this can be a warning to back off or to
start the backup.</div>
<div><br></div>
<div>Thanks again for all the input to this thread.</div>
<div><br></div>
<div>best</div>
<div><br></div>
<div>Hugh</div>
<div><br></div>
<div>At 11:47 -0800 18/1/10, Kent Osterberg wrote:</div>
<blockquote type="cite" cite>Hugh,<br>
</blockquote>
<blockquote type="cite" cite>You may be interested in this article
&quot;A critical review of using the Peukert equation for determining
the remaining capacity of lead-acid and lithium-ion batteries&quot; by
Dennis Doerffel and Suleiman Abu Sharkh from the School of Engineering
Sciences, University of Southampton.&nbsp; It is available from <a
href=
"http://www.sciencedirect.com/science?_ob=ArticleURL&amp;_udi=B6TH1-4GG2J4C-8&amp;_user=10&amp;_coverDate=04%2F21%2F2006&amp;_rdoc=1&amp;_fmt=high&amp;_orig=browse&amp;_sort=d&amp;view=c&amp;_acct=C000050221&amp;_version=1&amp;_urlVersion=0&amp;_userid=10&amp;md5=2b8498cbb0415fe6dda0e003c6a23598"><span
></span>http://www.sciencedirect.com/science</a> for a small fee.&nbsp;
If the link does not work, just search for the lead author's last
name.<br>
<br>
The authors describe testing lead acid batteries at high rates of
discharge from fully discharged down to the point that the terminal
voltage is 10.0 volts.&nbsp; After letting the batteries rest, they
continued to discharge further at a lower rate until the terminal
voltage was again 10.0 volts.&nbsp; Results were compared to
discharging at the slow rate only.&nbsp; The total amphours delivered
when a low discharge rate follows a high discharge were less by 5 to
10%.&nbsp; With 10% associated with a C2 and C/20 discharge of a 17 AH
battery and 5% associated with a C/1.2 and C/13 discharge of a 65 ah
battery.</blockquote>
<blockquote type="cite" cite><br>
In short, the capacity loss indicated by Peukert only applies to a
continuous discharge rate.&nbsp; When a slow discharge follows a rapid
discharge, the total number of amphours delivered is almost the same
(just 5 to 10% less) as if the discharge happened at entirely at the
slow rate.&nbsp; If you were estimating how far your electric car
would travel, that 5 or 10% may be critical.&nbsp; For the rates of
discharge and depths of discharge normally used for off-grid homes the
&quot;lost&quot; capacity is probably even less.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>
</blockquote>
<blockquote type="cite" cite><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: RE-wrenches@lists.re-wrenches.org<br>
<br>
Options &amp; settings:<br>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br
>
<br>
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br>
<br>
List rules &amp; etiquette:<br>
www.re-wrenches.org/etiquette.htm<br>
<br>
Check out participant bios:<br>
www.members.re-wrenches.org</blockquote>
<div><br></div>
<div><br></div>
<x-sigsep><pre>-- 
</pre></x-sigsep>
<div>Hugh Piggott<br>
<br>
Scoraig Wind Electric<br>
Scotland<br>
http://www.scoraigwind.co.uk</div>
</body>
</html>