<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN">
<html>
<head>
  <meta content="text/html;charset=ISO-8859-1" http-equiv="Content-Type">
  <title></title>
</head>
<body bgcolor="#ffffff" text="#000000">
Drake,<br>
<br>
The spreadsheet name was Peukert.xls and all it computed was the
Peukert effect - greater discharge current &lt;-&gt; smaller battery
capacity.&nbsp; Peukert's equation is based on a constant discharge current
from fully charged to fully discharged (10.5 volts at the current in
question).&nbsp; The misunderstanding (almost urban myth) comes when
considering what happens when a battery is subject to partial (or even
complete) discharge at a high current.&nbsp; The amphours accrued at a high
discharge rate actually have little effect on the total amphours that
can be delivered at a low discharge rate.<br>
<br>
Example:<br>
Brand XYZ L-16 battery battery has a capacity of 400 Ah @ C/20 or 300
Ah @ C/6.<br>
There's a 25% difference between these two capacities.<br>
>From a full battery, discharge at 50 amps until the voltage is 10.5
volts, that takes 300 Ah.&nbsp; <br>
The battery is functionally dead, 100% DOD, if we need 50 amps at more
than 10.5 volts.<br>
But at 20 amps the battery is not dead.&nbsp; The battery will still deliver
another 80 Ah for a total of 380 Ah (5% less than 400 Ah @ C20) before
the voltage gets down to 10.5 volts.<br>
<br>
The 380 Ah and 5% numbers here are just for example purposes; if you
did this test to a L-16 the total would probably be higher than 380 Ah,
but you certainly would get less than 400 Ah.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc<br>
<br>
<br>
Drake Chamberlin wrote:
<blockquote
 cite="mid:20100119181758.C2AEB5F574@friskymail-a1.g.dreamhost.com"
 type="cite">Kent, <br>
  <br>
At 12:34 PM 1/19/2010, you wrote:<br>
  <blockquote type="cite" class="cite" cite="">In the tests performed
by Dennis
Doerffel and Suleiman Abu Sharkh it is was in the five to ten percent
range.</blockquote>
  <br>
In the first Excel spreadsheet, posted by Julie Haugh, the loss rates
seem a lot higher than five to ten percent.&nbsp; Using 220 AH battery,
for example, I used a 50 amp discharge rate. The result was that there
would be about 140 AH available.&nbsp; That would amount to a 37% loss of
capacity.&nbsp; <br>
  <br>
Is it your thinking that this high result is due to the low terminal
voltage at that point, and that the remaining AH would be available
after
the battery terminal voltage had a chance to recover?&nbsp;&nbsp; Is the
attached spreadsheet just incorrect?<br>
  <br>
Thanks,<br>
  <br>
  <br>
  <x-sigsep></x-sigsep>
  <p><font color="#0000ff">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font color="#0000ff" size="1">TM&nbsp;
  </font><font color="#0000ff">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></p>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
  <pre wrap="">
<hr size="4" width="90%">

No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a> 
Version: 9.0.730 / Virus Database: 270.14.150/2632 - Release Date: 01/18/10 23:34:00

  </pre>
</blockquote>
</body>
</html>