<font size=3>Dick:<br><br>
Just to follow up, below is the reply I received from the inspector when
I asked for clarification.&nbsp; I had asked for clarification because I
admit ignorance to this section and I wanted to formulate a good response
on the first attempt:<br><br>
<i>There must be a main disconnect for panel C in the pump house. A
main<br>
circuit breaker in panel C would satisfy this requirement. If the
panel<br>
does not have a main circuit breaker (MLO) a maximum of six branch
circuits<br>
are allowed per NEC 225.33.<br><br>
</i>I prefer to approach these requirements with generic solutions.&nbsp;
The broader a solution, the more likely it will apply to other
projects.&nbsp; Also, a generic solution can box you in to a certain
design.&nbsp; I did not know the number of circuit breakers and did not
want to drive out to the job to find out.&nbsp; Instead I put this note
on the plans:<br><br>
<i>4. Panel C shall have 6 or fewer circuit breakers or implement
Documented Safe Switching Procedures per 225.32 Exception 1.<br><br>
</i>This proved to be acceptable and a permit was issued a few days
ago.&nbsp; I have since found out that there are 5 existing
breakers.&nbsp; One is in the off position and may be a spare.&nbsp; We
will be installing two inverters, bringing the number of breakers to
7.&nbsp; If I can remove one breaker, I achieve compliance that way. If I
can not remove a breaker, I write up a procedure, post it and I'm
good.<br><br>
Thanks for your input.<br><br>
William Miller<br><br>
<br><br>
At 06:33 PM 12/11/2009, you wrote:<br>
<blockquote type=cite class=cite cite>William,<br><br>
No, I mean what is your problem with complying with the request,
&quot;Show the<br>
number of existing circuits and/or the&nbsp; <br>
disconnecting means for panel C&quot;. Why not just do that?<br><br>
Dick<br><br>
<br><br>
--- You wrote:<br>
Dick:<br><br>
I too am mystifed.&nbsp; I sent a request for clarification but have
not&nbsp; <br>
heard back.&nbsp; It may be some kind of power trip as we have been at
odds&nbsp; <br>
over many issues.&nbsp; I will report back.<br><br>
William Miller<br>
Millersolar.com<br><br>
On Dec 11, 2009, at 6:05 PM, Richard.L.Ratico@VALLEY.NET (Richard L&nbsp;
<br>
Ratico) wrote:<br><br>
&gt; William,<br>
&gt;<br>
&gt; No direct specific experience with this, but, respectfully, what
is&nbsp; <br>
&gt; the problem?<br>
&gt; The code sections seem clear and not unreasonable nor arduous.<br>
&gt;<br>
&gt; Dick Ratico<br>
&gt; Solarwind Electric<br>
&gt;<br>
&gt;<br>
&gt; --- You wrote:<br>
&gt; Friends:<br>
&gt;<br>
&gt;<br>
&gt; I just received a plan correction for a grid-tie permit
application&nbsp; <br>
&gt; wherein<br>
&gt; the inspector is questioning compliance with section 225.&nbsp;
Below is&nbsp; <br>
&gt; the<br>
&gt; text of the correction notice:<br>
&gt;<br>
&gt; The existing panel C in the pump house must comply with NEC 225.31.
225.32<br>
&gt; &amp; 225.33. Show the number of existing circuits and/or the&nbsp;
<br>
&gt; disconnecting<br>
&gt; means for panel C.<br>
&gt;<br>
&gt; Has anyone ever had experience with this section being applied to
a<br>
&gt; grid-tie system?&nbsp; The inverters will be inside a pump house
remote&nbsp; <br>
&gt; from the<br>
&gt; main residence.<br>
&gt;<br>
&gt; Thanks in advance.<br>
&gt;<br>
&gt; William Miller<br>
&gt;<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 9.0.716 / Virus Database: 270.14.103/2558 - Release Date:
12/11/09 02:06:00</blockquote>