<div>On this area of Northern New York i have not had over .30 KWH(300 watts)per day over the last week.... and thats the high day, most have been .10 or none, none being the most common. Thats off a 1400 watt rack of SW panels</div>

<div></div>
<div>Up here you size in a generator or go south for the winter. </div>
<div></div>
<div>Tell me again why i live here, any thoughts Roy? You can&#39;t be doing any better....</div>
<div></div>
<div>Bob<br><br></div>
<div class="gmail_quote">On Thu, Dec 10, 2009 at 9:29 AM, Darryl Thayer <span dir="ltr">&lt;<a href="mailto:daryl_solar@yahoo.com">daryl_solar@yahoo.com</a>&gt;</span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">The system is way short on PV, and I would think that it is already a Gen with PV support. I agree with everybody more PV is the way to go but the batteries must be cooked by now with this many Deep cycles. BTW C/10 is not important, in fact I feel better if I charge slower. I know fast charging is a good way to kill batteries. Operating cost needs a high efficiency engine. So until you can get the PV up to become the dominant source, a gen is probibly in order. I tend to use smaller generators than most people, and the fuel efficency of a Honda inverter gen is hard to beat.<br>
<br>--- On Thu, 12/3/09, <a href="mailto:Windsun@wind-sun.com">Windsun@wind-sun.com</a> &lt;<a href="mailto:windsun@wind-sun.com">windsun@wind-sun.com</a>&gt; wrote:<br><br>&gt; From: <a href="mailto:Windsun@wind-sun.com">Windsun@wind-sun.com</a> &lt;<a href="mailto:windsun@wind-sun.com">windsun@wind-sun.com</a>&gt;<br>

<div class="im">&gt; Subject: Re: [RE-wrenches] Off-Grid Sizing Case<br></div>&gt; To: &quot;RE-wrenches&quot; &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>&gt; Date: Thursday, December 3, 2009, 12:18 PM<br>
&gt;<br>&gt; Off-Grid Sizing Case<br>
<div>
<div></div>
<div class="h5">&gt;<br>&gt;<br>&gt;<br>&gt;<br>&gt;<br>&gt; The rate of charging is not the<br>&gt; real problem in most<br>&gt; undersized systems, it is the fact that the batteries<br>&gt; seldom, if ever, get fully<br>
&gt; charged. Given the ratio of PV vs battery capacity, I would<br>&gt; suspect that their<br>&gt; batteries have been chronically undercharged for ages. We<br>&gt; usually recommend<br>&gt; around 1 watt of pvper AH for a 12 volt system, 2<br>
&gt; watts for 24 volt<br>&gt; etc.<br>&gt; <br>&gt; A generator is not usually the<br>&gt; answer, because it may<br>&gt; have to run for hours to get that final 5-15% of charge<br>&gt; into the batteries.<br>&gt; Generators are good for equalizing, not so much for general<br>
&gt;<br>&gt; charging.<br>&gt; <br>&gt; ..................................................................................................<br>&gt; Northern<br>&gt; Arizona Wind &amp; Sun - Electricity From The Sun Since<br>
&gt; 1979<br>&gt; Solar Discussion<br>&gt; Forum: <a href="http://www.wind-sun.com/ForumVB/" target="_blank">http://www.wind-sun.com/ForumVB/</a><br>&gt; ..................................................................................................<br>
&gt;<br>&gt;  ----- Original Message<br>&gt; -----<br>&gt;  From:<br>&gt;  Mark<br>&gt;  Frye<br>&gt;  To: &#39;RE-wrenches&#39;<br>&gt;<br>&gt;  Sent: Thursday,<br>&gt; December 03, 2009 10:56<br>&gt;  AM<br>&gt;  Subject: Re:<br>
&gt; [RE-wrenches] Off-Grid<br>&gt;  Sizing Case<br>&gt;<br>&gt;<br>&gt;  So being able to achieve C10<br>&gt; charging from the PV is not so<br>&gt;  important?<br>&gt;<br>&gt; Mark<br>&gt; Frye<br>&gt; Berkeley Solar<br>
&gt; Electric<br>&gt;  Systems<br>&gt; 303 Redbud<br>&gt;  Way<br>&gt; Nevada<br>&gt;  City, CA 95959<br>&gt; (530) 401-8024<br>&gt; <a href="http://www.berkeleysolar.com/" target="_blank">www.berkeleysolar.com</a><br>
&gt;  <br>&gt;<br>&gt;<br>&gt;<br>&gt;  From: <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a><br>&gt;<br>&gt;  [mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>] On<br>
&gt; Behalf Of <a href="mailto:Windsun@wind-sun.com">Windsun@wind-sun.com</a><br>&gt; Sent:<br>&gt;  Thursday, December 03, 2009 9:51 AM<br>&gt; To:<br>&gt;  RE-wrenches<br>&gt; Subject: Re: [RE-wrenches] Off-Grid Sizing<br>
&gt;  Case<br>&gt;<br>&gt;<br>&gt;<br>&gt;  I would go with #1.<br>&gt; The solar is obviously<br>&gt;  undersized for the battery bank he has. Another panel +<br>&gt; MPPT should give him<br>&gt;  about 25-40% more, depending on temps etc.<br>
&gt;  <br>&gt;<br>&gt; ..................................................................................................<br>&gt; Northern<br>&gt;  Arizona Wind &amp; Sun - Electricity From The Sun Since<br>&gt; 1979<br>
&gt; Solar<br>&gt;  Discussion Forum: <a href="http://www.wind-sun.com/ForumVB/" target="_blank">http://www.wind-sun.com/ForumVB/</a><br>&gt; ..................................................................................................<br>
&gt;<br>&gt;<br>&gt;<br>&gt;  _______________________________________________<br>&gt; List sponsored by<br>&gt;  Home Power magazine<br>&gt;<br>&gt; List Address:<br>&gt;  <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;<br>&gt; Options &amp;<br>&gt;  settings:<br>&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
&gt;<br>&gt; List-Archive:<br>&gt;<br>&gt; <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>&gt;<br>&gt; List<br>
&gt;  rules &amp; etiquette:<br>&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>&gt;<br>&gt; Check out<br>&gt;  participant<br>&gt; bios:<br>&gt; <a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
&gt;<br>&gt;<br>&gt;<br></div></div>&gt; -----Inline Attachment Follows-----<br>
<div>
<div></div>
<div class="h5">&gt;<br>&gt; _______________________________________________<br>&gt; List sponsored by Home Power magazine<br>&gt;<br>&gt; List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
&gt;<br>&gt; Options &amp; settings:<br>&gt; <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>&gt;<br>
&gt; List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>&gt;<br>&gt; List rules &amp; etiquette:<br>
&gt; <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>&gt;<br>&gt; Check out participant bios:<br>&gt; <a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
&gt;<br>&gt;<br><br><br><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
<br></div></div></blockquote></div><br>