Portable generators do not usually ground to a premise wiring
system.&nbsp; The neutral and equipment ground bond to the frame.&nbsp; I
don't know how safe or unsafe it is, but that is normal operation for
these machines.&nbsp;&nbsp; This method is required by 250.34, and is
acceptable for cord and plug applications, which this is. <br><br>
At 11:49 AM 11/12/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">At 10:08 -0500 12/11/09, Drake
Chamberlin wrote:<br>
<blockquote type=cite class=cite cite=""><br><br>
Using a 3 to 2 prong adaptor might be the best solution where code
rigidity is not the norm.</blockquote><br>
As I understand it, this removes the grounding wire that linked the
genset to the house.&nbsp; If the neutral wire comes loose, then you are
almost guaranteed to have a lethal voltage between the generator frame
and house ground.&nbsp;&nbsp; That doesn't seem likely to be the safest
solution although it might be the simplest to install.<br>
-- <br>
Hugh Piggott<br><br>
Scoraig Wind Electric<br>
Scotland<br>
<a href="http://www.scoraigwind.co.uk/" eudora="autourl">
http://www.scoraigwind.co.uk</a><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a><br>
</blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font size=1 color="#0000FF">TM&nbsp;
</font><font color="#0000FF">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>