For a test, install a three prong to two prong adaptor on the attachment
plug, and see if the problem persists.&nbsp; The neutral to ground bond
is likely made in the generator as well as in the electrical service.
This will cause a current in the equipment ground, which will trip a
GFCI.&nbsp;&nbsp; It might be possible to undo the neutral to ground bond
in the generator.  <br><br>
Drake <br><br>
At 07:10 PM 11/10/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">Fellow Wrenches,<br><br>
On an off the grid system we did for a client a year or two back,
we&nbsp; <br>
installed an Outback VFX3524 mounted on a Midnight Solar E
Panel.&nbsp;&nbsp; <br>
They had a manual pull Homelight generator as back up.&nbsp; All worked
well.<br>
Recently the client upgraded to an electric start 8000 watt Generac&nbsp;
<br>
generator.<br>
Now every time they start the new generator, the GFI 20 amp&nbsp; <br>
receptacle on the generator pops.<br>
There is probably a redundant neutral to ground bond that is
causing&nbsp; <br>
this but I am uncertain on the best approach to remedy this
condition<br>
Any recommendations or experience on how to get the generator to&nbsp;
<br>
interface with the system?<br><br>
Thanks<br>
Larry<br><br>
Larry Brown<br>
Sun Mountain _______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font size=1 color="#0000FF">TM&nbsp;
</font><font color="#0000FF">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>