In addition to ramping down the charge amps, you also need to ensure that
the loads are removed for testing.&nbsp; Even with charge amp at 1, if
the loads exceed the capabilities of the generator to maintain adequate
voltage and frequency.<br><br>
I discussed this very issue with Outback at the show yesterday.&nbsp; The
GFX series inverter has tighter input tolerances on the AC input.&nbsp;
This is because there is only one AC input and that input needs to comply
with grid tie requirements.<br><br>
Another short coming of the Outback is: if the loads exceed the source
capabilities, once the transfer occurs, the source will overload, be it
to trip a source breaker or bog down a generator.&nbsp; If this were an
SW or XW inverter, the inverter would synchronize with the source and
assist in delivering power to the loads.<br><br>
William<br><br>
<br><br>
<br>
At 12:07 PM 10/30/2009, you wrote:<br>
<blockquote type=cite class=cite cite>Hi Drake-<br><br>
You may be overloading the genny (and it either pops a reset breaker
or<br>
just shows a red light that there is an internal overload, requiring
you<br>
cycle the on/off switch to reset.<br><br>
To &quot;test&quot; I suggests ramping down the charging AC amps on the
mate to 1 or<br>
so, see if the genny charges, then step up the charger amps until the
unit<br>
cuts out.&nbsp; Kinda like the Appalachian torque wrench: tighten until
the SS<br>
bolt breaks off, then back it off 1/2 turn.<br>