<font size=3>Mick:<br><br>
Even with the upgrade there are still not enough slots.&nbsp; To do a
complete job you need the following 2 pole breakers:<br><br>
Inverter out X 3<br>
Inverter Grid in X 3<br>
Inverter Gen in X 3<br>
Grid Bypass X 1<br>
Gen Bypass X 1<br>
System output X 1 (minimum)<br><br>
The above requires 12 spaces.&nbsp; The new plate will fit only 9 2 pole
QOU breakers.<br><br>
There are other considerations:<br><br>
The largest QOU breaker made is 125 A.&nbsp; Three XW inverters will
through-transfer 180 amps, so a 125A breaker will create a bottle
neck.<br><br>
Xantrex does not&nbsp; (nor does anyone else) offer any means to select
from two AC sources for bypass.&nbsp; Think about it:&nbsp; if you
purchase a three XW system because the inverters offer two AC inputs, you
are screwed because there are no internal bypass options.&nbsp; You can
offer to provide bypass with the generator OR the grid, not both, and it
requires an external transfer switch.&nbsp; See page 2-37 in the
manual.&nbsp; Figure 2-30 offers a grid source bypass but requires the
external transfer switch.&nbsp; What if the grid gets hit by lightening
and takes out your inverters?&nbsp; You can start the generator but you
can't get power to your customer's house.<br><br>
Fortunately there are work-arounds.&nbsp; We spent considerable time
thinking about this and we hope to market design packages to anyone who
wants a truly complete 3 stack XW system.&nbsp; Contact me off
line.<br><br>
William Miller<br><br>
<br>
At 07:25 AM 10/23/2009, you wrote:<br>
<blockquote type=cite class=cite cite>Addendum: the Xantrex XW power
distribution box now ships with more breaker slots on the AC
rail...enough to accommodate that third inverter mentioned by
William.<br><br>
There is a field upgrade kit available from Xantrex at no charge, for
those who have the old style box. This is a replacement DIN rail, new
dead front with more slots, fasteners, and even a drill bit to drill out
the original rivets.<br><br>
I have the contact name for the kit, in case anyone wishes to contact me
off list...or List participant Mark Edmunds would also have that
information.<br><br>
The upgrade process is a little sketchy, because the mounting holes on my
replacement DIN rain were slightly imperfect compared to the holes in the
box. That provides another use for the courtesy drill bit...<br><br>
Mick Abraham, Proprietor<br>
<a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>
Voice: 970-731-4675</font></blockquote></body>