I suggest that high rate recharge could be safely done but only with a charge algorithm more sophisticated than what is commonly found in renewable energy gear. <br><br>The chargers typically found in our industry deliver the same &quot;bulk&quot; charge amperage from initiation of the recharge all the way to when the absorption voltage is reached. So...if you set that for a high value the same high rate would be present not only when the battery is highly depleted but also when the battery is approaching 80% state of charge. That seems scary to me.<br>

<br>The electric vehicle industry may offer some good choices in chargers specifically for &quot;rapid recharge&quot;. These would deliver highest amps at first but would diminish the amperage as the battery voltage ramps up--without waiting for the absorption voltage to be reached before the amperage taper begins.<br>

<br>You might like to ask the technicians at your battery manufacturer to make sure they&#39;re OK with your intended recharge method. Regards to all,<br><br>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br>

<br>Voice: 970-731-4675<br>
<br><br><div class="gmail_quote">On Tue, Sep 15, 2009 at 9:11 AM, Walt Ratterman <span dir="ltr">&lt;<a href="mailto:wratterman@sunenergypower.com">wratterman@sunenergypower.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">











<div link="blue" vlink="purple" lang="EN-US">

<div>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Peter,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">The DEKA charging manual that I have been working from for their
sealed batteries (AGM and Gel) quote 30% of C20.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">And.DEKAs literature also has a maximum charging voltage of 2.35
VPC.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Not sure about the other brands.</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Thanks,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Walt</span></p><div class="im">

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Peter
Parrish<br>
<b>Sent:</b> Tuesday, September 15, 2009 7:33 AM<br>
<b>To:</b> &#39;RE-wrenches&#39;<br>
<b>Subject:</b> [RE-wrenches] Charging AGM Batteries</span></p>

</div>

</div>

<p></p>

</div><p><span style="font-size: 10pt; color: navy;">I have been told that AGM batteries can withstand pretty aggressive
charging rates, with a bulk rate being  of C/20. For example a MK 8A8D, with a
C/20 of 245 A-h, would start with 122 A. If this is okay, can I still use the
standard 14.6 V value for switching from Bulk to Absorb? What about ambient
temperature effects at high charge rates?</span></p><div><div></div><div class="h5">

<p><span style="font-size: 10pt; color: navy;"></span></p>

<p><span style="font-size: 10pt; color: navy;">We have need from time to time to charge AGMs as quickly as we can
safely do so, so any information on high charge rates would be appreciated.</span></p>

<p><span style="font-size: 10pt; color: navy;"></span></p>

<p><span style="font-size: 10pt; color: navy;">- Peter</span></p>

<div>

<p><span style="font-size: 10pt; color: navy;"></span></p>

<p><br clear="all">
</p>

<p><span style="font-size: 10pt; color: navy;">Peter T. Parrish, Ph.D., President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
CA Lic. 854779, NABCEP TM Cert. 031806-26<br>
<a href="mailto:peter.parrish@calsolareng.com" target="_blank">peter.parrish@calsolareng.com</a>
<br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885 </span><span style="font-size: 9pt; color: navy;"></span></p>

<p><span style="color: navy;"></span><span style="color: blue;"> </span></p>

</div>

</div></div></div>

</div>


<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>