<html><head><style type='text/css'>p { margin: 0; }</style></head><body><div style='font-family: Times New Roman; font-size: 12pt; color: #000000'>esteemed wrenches (or just steamed if youve been out in the hot lately)<div><br></div><div>I'm curious why more folks don't use the same flat roof ballasted rack approach for large ground mounts? &nbsp;Geotech weed barier and off we go... &nbsp;my initial calcs sat its a cost saver... my instinct says it viable, but my other instinct says "if it were this easy I would see it all the time (and I've never seen it)</div><div><br></div><div>what's up? &nbsp;frost heave/instability? &nbsp;wav-i-ness of the ground? better performance at steep angle worth all the extra cost (not according to my pencil with today's mod costs). &nbsp;Thoughts?&nbsp;<br><br>For a brighter energy future,<br><br>Geoff Greenfield<br>President<br>Third Sun Solar &amp; Wind Power Ltd.<br>340 West State Street, Unit 25<br>Athens, OH 45701<br><br>740.597.3111 &nbsp; &nbsp; Fax 740.597.1548<br>www.Third-Sun.com<br><br>Clean Energy - Expertly Installed<br><br><br><br><br><br><br>----- "Dave Click" &lt;daveclick@fsec.ucf.edu&gt; wrote:
<br>&gt; Thanks all.<br>&gt; <br>&gt; It was my understanding that we should still be running the conductors <br>&gt; of the same circuit through the same raceway, even if it is the DC input <br>&gt; into the inverter since that DC oscillates slightly (nowhere near as <br>&gt; much as AC). I wasn't concerned about eddy currents in the FNMC of <br>&gt; course but the metal box itself, a concern being voiced on this list <br>&gt; before. I'd be more concerned about this if it were a 1MW inverter <br>&gt; rather than a 7kW, but still.<br>&gt; <br>&gt; Thanks for the info on the GEC tap and I'm glad the split bolts work here.<br>&gt; <br>&gt; The conduit in question doesn't seem to be there just for physical <br>&gt; protection; the wire runs from the east end of the array for 100'+ and <br>&gt; only the last 3' are in conduit. If it were only for protection I'd be <br>&gt; fine with it being open-ended on both ends, but since it's there to feed <br>&gt; the conductors into the box, that's why I was treating it as a regular <br>&gt; conduit that required a cord grip at the other end. Where do others make <br>&gt; the distinction?<br>&gt; <br>&gt; Thanks,<br>&gt; DKC<br>&gt; <br>&gt; -------- Original Message --------<br>&gt; Subject: Re: [RE-wrenches] DC positive and negative in same conduit, <br>&gt; other inspection issues<br>&gt; From: Kelly Keilwitz, Whidbey Sun &amp; &nbsp;Wind &lt;kelly@whidbeysunwind.com&gt;<br>&gt; To: RE Wrenches listserve &lt;re-wrenches@lists.re-wrenches.org&gt;<br>&gt; Date: 2009/8/19 21:10<br>&gt; <br>&gt; &gt; Dave,<br>&gt; &gt; Only GEC's are subject to the "continuous" rule (250.64C). It sounds like<br>&gt; &gt; your are talking about an EGC tapped from the GEC.<br>&gt; &gt; <br>&gt; &gt; When splicing PV GEC's required under 690.47D, either together (from<br>&gt; &gt; separated arrays) or to the existing AC GEC (if close enough), we have been<br>&gt; &gt; allowed to use split bolts instead of irreversible splices, per 250.64D1,<br>&gt; &gt; "Grounding Electrode Conductor Taps" (at end of paragraph). I.E., the<br>&gt; &gt; "continuous" rule is only being applied to the main GEC.<br>&gt; &gt; <br>&gt; &gt; I agree with Kurt on the LTNMF being used only as extra (not required) wire<br>&gt; &gt; protection for the USE-2. We often do this when running PV conductors<br>&gt; &gt; between short separations in modules or rails. I would think that only<br>&gt; &gt; temperature and fill corrections would apply - and only if the length<br>&gt; &gt; requires.<br>&gt; &gt; <br>&gt; &gt; -Kelly<br>&gt; &gt; <br>&gt; &gt; Kelly Keilwitz, P.E.<br>&gt; &gt; Whidbey Sun &amp; Wind, LLC<br>&gt; &gt; Renewable Energy Systems<br>&gt; &gt; NABCEP Certified PV Installer<br>&gt; &gt; 987 Wanamaker Rd, <br>&gt; &gt; Coupeville, WA 98239<br>&gt; &gt; PH &amp; FAX 360-678-7131<br>&gt; &gt; sunwind@whidbeysunwind.com<br>&gt; &gt; <br>&gt; &gt; On 8/19/09 2:41 PM, "Dave Click" &lt;daveclick@fsec.ucf.edu&gt; wrote:<br>&gt; &gt; <br>&gt; &gt;&gt; For the grounding electrode wiring, it seems that it's fine to me since<br>&gt; &gt;&gt; they ran the continuous #6 to each rail and then to the rod, qualifying<br>&gt; &gt;&gt; as the 690.47(D) supplemental electrode. But the split bolts tapping<br>&gt; &gt;&gt; that GEC to "ground the disconnect," these are required to be<br>&gt; &gt;&gt; irreversible connections to the ground bus in that disconnect, right?<br>&gt; &gt; <br>&gt; &gt; <br>&gt; &gt; &nbsp;<br>&gt; &gt; <br>&gt; &gt; <br>&gt; &gt; <br>&gt; &gt; _______________________________________________<br>&gt; &gt; List sponsored by Home Power magazine<br>&gt; &gt; <br>&gt; &gt; List Address: RE-wrenches@lists.re-wrenches.org<br>&gt; &gt; <br>&gt; &gt; Options &amp; settings:<br>&gt; &gt; http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br>&gt; &gt; <br>&gt; &gt; List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br>&gt; &gt; <br>&gt; &gt; List rules &amp; etiquette:<br>&gt; &gt; www.re-wrenches.org/etiquette.htm<br>&gt; &gt; <br>&gt; &gt; Check out participant bios:<br>&gt; &gt; www.members.re-wrenches.org<br>&gt; &gt; <br>&gt; &gt; <br>&gt; _______________________________________________<br>&gt; List sponsored by Home Power magazine<br>&gt; <br>&gt; List Address: RE-wrenches@lists.re-wrenches.org<br>&gt; <br>&gt; Options &amp; settings:<br>&gt; http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br>&gt; <br>&gt; List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br>&gt; <br>&gt; List rules &amp; etiquette:<br>&gt; www.re-wrenches.org/etiquette.htm<br>&gt; <br>&gt; Check out participant bios:<br>&gt; www.members.re-wrenches.org<br>&gt; <br>&gt; </div></div></body></html>