Nick,<br><br>
Where did you put the relay?&nbsp; I had problems breaking the AC out of
Sunny Boy inverters. <br><br>
Thanks,<br><br>
Drake<br><br>
<br>
At 07:58 PM 8/3/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">Aloha Solar Bozos:<br>
&nbsp;&nbsp;&nbsp; I haven't posted here in ages, and I hope I am cutting
out the appropriate stuff?&nbsp; Probably not, but I will give it a
try.&nbsp; I want to reply to Topic 3 regarding backfeeding an off-grid
inverter with a grid-tied inverter.<br>
&nbsp;&nbsp;&nbsp; In 2004, I back-fed a SWR-2500U into an Outback FX
inverter's back-up power panel.&nbsp; It required a transformer to step
down to 120VAC and a voltage controlled relay to shut the Sunny Boy off
when the batteries were charged.&nbsp; Greg at OB said that the inverters
would regulate the AC output voltage at ~120V, so when the voltage would
rise up from the Sunny Boy's production, the FX was forced to take the
power in, resulting in the batteries being charged.&nbsp; You probably
realize that the Sunny Island controls the grid-tied inverter's output
but fluctuating the Hertz, which eliminated that issue for them.<br>
<br>
<font face="Tahoma" size=2><b>From:</b>
&quot;re-wrenches-request@lists.re-wrenches.org&quot;
&lt;re-wrenches-request@lists.re-wrenches.org&gt;<br>
<b>To:</b> re-wrenches@lists.re-wrenches.org<br>
<b>Sent:</b> Monday, August 3, 2009 6:47:22 AM<br>
<b>Subject:</b> RE-wrenches Digest, Vol 2, Issue 818<br>
</font><br>
Send RE-wrenches mailing list submissions to<br>
&nbsp;&nbsp;&nbsp;
<a href="mailto:re-wrenches@lists.re-wrenches.org">
re-wrenches@lists.re-wrenches.org</a><br><br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
&nbsp;&nbsp;&nbsp;
<a href="http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org</a>
<br>
or, via email, send a message with subject or body 'help' to<br>
&nbsp;&nbsp;&nbsp;
<a href="mailto:re-wrenches-request@lists.re-wrenches.org">
re-wrenches-request@lists.re-wrenches.org</a><br><br>
You can reach the person managing the list at<br>
&nbsp;&nbsp;&nbsp;
<a href="mailto:re-wrenches-owner@lists.re-wrenches.org">
re-wrenches-owner@lists.re-wrenches.org</a><br><br>
When replying, please edit your Subject line so it is more specific<br>
than &quot;Re: Contents of RE-wrenches digest...&quot;<br><br>
<br>
When responding to posts within the Digest, be sure to restore the
Subject: line to the original, and please edit out any extraneous lines
from the quoted message.<br><br>
<br>
Today's Topics:<br><br>
&nbsp; 1. Re: AC Backfeed Battery Over-Charging (Jeff Yago)<br>
&nbsp; 2. Broken Modules (Doug Wells)<br>
&nbsp; 3. Re: AC Backfeed Battery Over-Charging (Tump)<br>
&nbsp; 4. Re: Broken Modules (Jeff Yago)<br><br>
<br>
----------------------------------------------------------------------<br>
<br>
Message: 1<br>
Date: Mon, 3 Aug 2009 06:21:56 -0700<br>
From: &quot;Jeff Yago&quot;
&lt;<a href="mailto:jryago@netscape.com">jryago@netscape.com</a>&gt;<br>
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging<br>
To: RE-wrenches
&lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">
re-wrenches@lists.re-wrenches.org</a>&gt;<br>
Message-ID:
&lt;<a href="mailto:20090803062156.CD9B16AE@resin17.mta.everyone.net">
20090803062156.CD9B16AE@resin17.mta.everyone.net</a>&gt;<br>
Content-Type: text/plain; charset=&quot;us-ascii&quot;<br><br>
An HTML attachment was scrubbed...<br>
URL:
&lt;<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/af3227a5/attachment-0001.htm">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/af3227a5/attachment-0001.htm</a>
&gt;<br><br>
------------------------------<br><br>
Message: 2<br>
Date: Mon, 3 Aug 2009 09:32:08 -0400<br>
From: Doug Wells
&lt;<a href="mailto:dwells@thesolarspecialists.com">
dwells@thesolarspecialists.com</a>&gt;<br>
Subject: [RE-wrenches] Broken Modules<br>
To:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br>
Message-ID:<br>
&nbsp;&nbsp;&nbsp;
&lt;<a href="mailto:D6573665-38CE-4E54-A70F-F7AC8F630DF3@thesolarspecialists.com">
D6573665-38CE-4E54-A70F-F7AC8F630DF3@thesolarspecialists.com</a>&gt;<br>
Content-Type: text/plain; charset=US-ASCII; format=flowed<br><br>
Wrenches,<br><br>
I am curious what other installers are doing with broken modules?<br>
I know some manufacturers are starting recycling programs.<br><br>
<br>
Doug Wells<br>
The Solar Specialists<br>
Morrisville, VT 05661<br>
(p) 802-223-7014<br>
(c) 802-498-5856<br>
<a href="http://www.thesolarspecialists.com">
www.thesolarspecialists.com</a><br><br>
<br><br>
<br><br>
<br><br>
------------------------------<br><br>
Message: 3<br>
Date: Mon, 3 Aug 2009 09:39:21 -0400<br>
From: &quot;Tump&quot;
&lt;<a href="mailto:tump@hughes.net">tump@hughes.net</a>&gt;<br>
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging<br>
To: &lt;<a href="mailto:jryago@netscape.com">jryago@netscape.com</a>&gt;,
&quot;'RE-wrenches'&quot;<br>
&nbsp;&nbsp;&nbsp;
&lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">
re-wrenches@lists.re-wrenches.org</a>&gt;<br>
Message-ID: &lt;CAFB0B2FF97B4386BB4EF00DF46766F9@tumpdggfbh2yn6&gt;<br>
Content-Type: text/plain; charset=&quot;us-ascii&quot;<br><br>
Hey Jeff this was something that Greg @ OB was working on summer of
06.....<br>
Should have it tump, almost got it little problem .... Ahhh sorry we are
no<br>
longer working on that! I was in the middle of a large AC Coupled system
&amp;<br>
had been waiting for 4 months for this &quot;trick&quot; soft ware to
come on line.<br>
Perhaps CF might be able to update us on this software. Kinda of a
no<br>
brainier perhaps, John B &amp; the boys @ SMA patented this
&quot;trick&quot; software.<br><br>
<br>
&nbsp;&nbsp;&nbsp;
&lt;<a href="mailto:Tump@swnl.net" eudora="autourl">
mailto:Tump@swnl.net</a>&gt;
<a href="mailto:Tump@swnl.net">Tump@swnl.net</a>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&lt;<a href="http://www.swnl.net/" eudora="autourl">
http://www.swnl.net/</a>&gt;<br>
<a href="http://www.SWNL.net">www.SWNL.net</a><br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Solarwinds
Northernlights&nbsp; <br>
&nbsp; Serving Mid Coast Maine &amp; Northern California<br>
&nbsp;&nbsp;&nbsp; Me.# 207-832-7574&nbsp; Cl.#&nbsp;
610-517-8401<br><br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
Blair &quot;TUMP&quot; May<br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; ********&nbsp; MAINE'S CHARTER
********<br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
NABCEP&nbsp;&nbsp;&nbsp; &quot;Certified PV Installer&quot; <br>
&nbsp; <br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; ********&nbsp; MAINE'S CHARTER
********<br>
&nbsp; Trace Xantrex &quot;Certified&quot; Dealer / Installer&quot;<br>
&nbsp; <br>
&nbsp; <br><br>
-----Original Message-----<br>
From:
<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a><br>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of Jeff
Yago<br>
Sent: Monday, August 03, 2009 9:22 AM<br>
To: RE-wrenches<br>
Subject: Re: [RE-wrenches] AC Backfeed Battery Over-Charging<br><br>
<br>
I have a question that may be one of those that everyone wants to know
the<br>
answer but feel they are the only one that doesn't know the answer,
or<br>
perhaps I am the only one that doesn't know!.&nbsp; <br><br>
In an AC-coupled system, i.e. the 240 VAC output solar inverter mounted
at a<br>
distant array (240 VAC out to reduce long line loss) is wired to the
120/240<br>
VAC output emergency panel supplied from a battery based inverter.&nbsp;
This<br>
allows the solar inverter to stay up when the grid goes down since it
thinks<br>
the grid is still up on the load side of the battery based
inverter.&nbsp; The<br>
battery based inverter will use any excess backfed power from the
solar<br>
inverter that is in excess of the other supplied loads to re-charge
the<br>
battery.&nbsp; However, when this happens the battery charging process
can boil<br>
the batteries when there are no other loads running.&nbsp; <br><br>
I have been told this is because the battery based inverter does not<br>
regulate its charging of the battery when using backfed power from
its<br>
output panel, but I still don't understand why.&nbsp; If the battery
charger in<br>
the inverter can provide regulated 3-stage battery charging when the
power<br>
is supplied from the grid or a generator, why does it suddenly become a
full<br>
output un-regulated battery charger when power is supplied from backfeed
and<br>
will keep charging regardless of reaching a high battery
voltage?&nbsp;&nbsp;&nbsp; <br><br>
I would have assumed the battery charger section would charge the same
way<br>
regardless of where the power is being supplied from, or perhaps
just<br>
shutdown on some kind of backfeed safety.&nbsp; As far as I know,
this<br>
over-charging problem in an AC coupled dual inverter system is true for
all<br>
battery-based inverters.&nbsp; Any inverter techs out there that can
explain<br>
why?&nbsp; Perhaps this would be a nice feature in future high-end
battery-based<br>
inverters so we no longer need the custom power relay field wiring
to<br>
provide this high voltage cut-out?.<br><br>
Thanks,<br><br>
Jeff Yago<br><br>
<br><br>
&nbsp; _____&nbsp; <br><br>
Netscape.&nbsp; Just the Net You Need.<br><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL:
&lt;<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/040f6858/attachment-0001.htm">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20090803/040f6858/attachment-0001.htm</a>
&gt;<br><br>
------------------------------<br><br>
Message: 4<br>
Date: Mon, 3 Aug 2009 06:47:21 -0700<br>
From: &quot;Jeff Yago&quot;
&lt;<a href="mailto:jryago@netscape.com">jryago@netscape.com</a>&gt;<br>
Subject: Re: [RE-wrenches] Broken Modules<br>
To: RE-wrenches
&lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">
re-wrenches@lists.re-wrenches.org</a>&gt;<br>
Message-ID:
&lt;<a href="mailto:20090803064721.CD9B1303@resin17.mta.everyone.net">
20090803064721.CD9B1303@resin17.mta.everyone.net</a>&gt;<br>
Content-Type: text/plain; charset=&quot;UTF-8&quot;<br><br>
We have only had one broken module due to shipping damage and this was
the bottom 200 watt module in a shipment where each 2 modules on the
pallet were in heavy cardboard shipping boxes.&nbsp; Of course this not
discovered for several weeks until we worked our way down the
stack.&nbsp; However, since suppliers like Evergreen have switched to the
plasic corners that allow stacking modules without any cardboard
packaging, we have had no more breakage in shipment.&nbsp; I assume the
fork truck drivers now see a large stack of glass and take a little more
care whenre thay ram the forks. <br><br>
As far as what we did with our broken module (which taught a very
expensive lesson about checking shipments), we keep it to show students
in our training classes what happens when things go wrong.<br><br>
Jeff Yago<br><br>
_____________________________________________________________<br>
Netscape.&nbsp; Just the Net You Need.<br><br>
<br>
------------------------------<br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br><br>
End of RE-wrenches Digest, Vol 2, Issue 818<br>
*******************************************<br><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP </font><font size=1 color="#0000FF">TM&nbsp;
</font><font color="#0000FF">Certified PV Installer <br>
Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>