<font size=3>Dick:<br><br>
Regardless, the code requires that all portions of the circuit
accommodate the sum of the over current devices supplying the
circuit.&nbsp; The citation is below.<br><br>
I am not defending the code, I am telling you what I believe it
says.&nbsp; You don't need to sell your view point to me, you need to
sell it your local building officials.&nbsp; My goal is to interpret the
code such that my designs are unassailable by building officials.&nbsp; I
don't want unpleasant surprises after I have signed a contract and begun
work for a fixed price.<br><br>
<i>690.64(B)(2) The sum of the ampere ratings of overcurrent devices in
circuits supplying power to a busbar or conductor shall not exceed the
rating of the busbar or conductor. (2002).&nbsp; <br><br>
</i>William Miller<br><br>
<br>
At 01:15 PM 8/2/2009, you wrote:<br>
<blockquote type=cite class=cite cite>Wlliam,<br><br>
If there were to be a short circuit in the feeder or the main service
panel (<br>
the one with no extra breaker spaces ), the solar's maximum 50 amp
contribution<br>
would be about the last thing to be concerned about. A short is going to
result<br>
in perhaps 1000s of amps coming from the grid into the short. The service
100<br>
amp breaker will trip immediately and clear the fault. The inverter will
lose<br>
the grid and drop offline. End of story.<br><br>
Dick<br><br>