<font size=3>Dick:<br><br>
I don't believe you have solved Brian's dilemma yet.&nbsp; It is my
understanding that if one is going to install a load side tape, the back
feed calculations need to work for every link of the distribution system
upstream to the meter.&nbsp; In the scenario you suggest, that will not
be the case.&nbsp; The 100 amp meter main on Brian's project will
still&nbsp; accept only 20 amps of PV AC feed, still not satisfying his
requirements.<br><br>
I may not have read Brian's original post closely enough.&nbsp; If Brian
needs to feed 40 amps of PV derived AC and he wants to do it via the load
side connection allowed by 690.63 (B), he has two choices:&nbsp;
<br><br>
<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab>A. He can
upgrade all of the distribution to 200 amps&nbsp; from the meter to his
point of connection.&nbsp; The arithmetic is simple:&nbsp; 200 * 120% =
240 amps.&nbsp; 240 -200 = 40 amps of PV feed allowed.<br>
<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab>B. He can
upgrade all of the distribution to at least 125 amps capability and leave
the 100 amp main breaker.&nbsp; This would require that all of his
distribution be upgraded, from the bus in the main disconnect to the
feeder wire to the sub-panels. 125 * 120% = 150 amps. 150 - 100 = 50 amps
of PV feed allowed.<br><br>
Logistically, there is not a lot if difference between A and B.<br><br>
See our web site,
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com/</a>,
for a point-of-connection calculator.&nbsp; <br><br>
Thanks for the advice on Milbank.&nbsp; I will not be needing any 200 amp
breakers as there is no need to up-size a breaker, instead I would be
generating more spare 200 amp main breakers.<br><br>
William<br><br>
<br>
At 12:20 PM 8/1/2009, you wrote:<br>
<blockquote type=cite class=cite cite>William,<br><br>
I stand corrected. Thank you. <br><br>
This is not a supply side tap. I should have said it was a tap on the
supply<br>
side of the panelboard main breaker. That said , I think it works and
meets<br>
code, provided the conductors spliced to the feeder are properly sized.
The<br>
panelboard busbar is protected by it's main breaker and cannot be
overloaded by<br>
the solar contributuion. <br><br>
On your other point, Milbank makes a 200 amp MMC that that can be
retrofitted<br>
with a 100 amp breaker. I have done this twice, but not because of a
solar<br>
install. We've had a couple 100 Amp, 300', underground service laterals
that<br>
required oversized conductors because of voltage drop. The Milbank 100
Amp<br>
equipment is physically too small to do this. In both cases we replaced
the very<br>
expensive 200 amp breaker with an also very expensive 100 amp breaker,
all by<br>
Milbank and labeled as such. I was told by my supplier it was impossible
to<br>
purchase a 200 amp Milbank MMC with the 100 A breaker preinstalled. The
100 A<br>
breaker is the same physical size as the 200 and fits right in, no
modifications<br>
required. I have two 200 amp Milbank breakers on my shelf if you need
them. The<br>
MMC units are very expensive to begin with. Here in VT / NH a basic meter
only<br>
enclosure is more often pared with a separate disconnect enclosure
through an<br>
offset or straight nipple. This combination might work for you,
substituting a<br>
load center for the disconnect.<br><br>
Dick Ratico<br>
Solarwind Electric</font></blockquote></body>