size=2 face=Arial>See Article 220 for load calculation and resulting breaker 
sizing requirments.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=296140917-31072009></SPAN>&nbsp;<BR><SPAN 
lang=en-us><FONT size=2 face=Arial>Mark Frye</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT size=2 face=Arial>Berkeley Solar Electric Systems</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>303 Redbud Way</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada City,&nbsp; CA 
95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>(530) 
401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial>&nbsp;</FONT></SPAN> </DIV>
<DIV>&nbsp;</DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Mendocino 
Solar Service<BR><B>Sent:</B> Friday, July 31, 2009 9:57 AM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> [RE-wrenches] down-sizing main 
breaker<BR></FONT><BR></DIV>
<DIV></DIV>Hi Folks,
<DIV><BR></DIV>
<DIV>Can anyone provide code reference or advice on this question?</DIV>
<DIV>Our customer has 100 amp service at the meter pedestal, 100 amp main 
breaker feeding 200 foot underground run to a 100 amp panel at the house. We 
need to land a 40 amp breaker, so are proposing to replace main panel at house 
with 200 amp panel. The AHJ says we need a 200 amp main breaker in this panel, 
which will work, but says this requires upsizing the feeder, main breaker at 
meter, and therefore utility service to 200 amps.</DIV>
<DIV><BR></DIV>
<DIV>I've read on this list and elsewhere about downsizing the main breaker in a 
panel to create capacity to make the 120% rule. This AHJ says you can't put in a 
breaker smaller than the panel size, and furthermore, everything upstream would 
have to be upsized. Is this from the code?<BR><BR>
<DIV><SPAN 
style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 14px Palatino; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0" 
class=Apple-style-span>
<DIV>Bruce Erickson</DIV>
<DIV>Mendocino Solar Service</DIV>
<DIV>PO Box 1252</DIV>
<DIV>Mendocino, CA 95460</DIV>
<DIV>707-937-1701</DIV>
<DIV><BR class=webkit-block-placeholder></DIV></SPAN><BR 
class=Apple-interchange-newline></DIV><BR></DIV></BODY></HTML>