According to a document I received from an F-P technician, here is what
it takes to run their washers on an inverter: I passed this document on
to the list late last year, so check your attachments folder for <br>
Using 120V Alternate Energy Generation.doc<br><br>
Are There Existing Customers who are Successfully&nbsp; Running a Smart
Drive Autowasher From An Inverter Supply?<br>
&nbsp;<br>
There are many installations where Smart Drive Autowashers are
successfully operating on an inverter supply.&nbsp; In our experience if
the following technical criteria are met&nbsp; by an inverter then
operation and reliability should not be an issue:<br>
&nbsp;<br>
RMS Voltage:&nbsp; 120V +/- 10%&nbsp; (up to -20% may still work provided
the pump outlet hose is not too high i.e. pumping a high head of
water)<br>
Frequency:&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 60 Hz +/- 5%<br>
Peak Voltage:&nbsp; 200V peak - <i> This is the major point!!!<br>
</i>Older style inverters can have an rms voltage inside specification
but do so by having short duration high voltage pulses.&nbsp; The Smart
Drive treats this high voltage pulse as a voltage transient and clamps
the voltage above 200V.&nbsp; The electronics are well rated to absorb
this clamp energy on a transient basis but not 120 times a second&nbsp;
(60Hz) continuously.&nbsp; If this continuous clamping occurs then it may
lead to premature failure of the Smart Drive electronics or the Inverter
electronics.<br>
Power Rating:&nbsp; 2kVA (2,000VA) minimum.<br>
While the Smart Drive only consumes about 650W of power maximum, the VA
rating can exceed 1kVA.&nbsp; Successful installations have a rating of
2kVA min.<br><br>
<br>
Allan Sindelar wrote at 04:41 PM 7/1/2009:<br>
&nbsp;<br>
<blockquote type=cite class=cite cite="">
<font face="Times New Roman, Times">According to others on this list, the
sine wave Magnum won\u2019t run one, so I would be very cautious.<br>
Allan<br>
&nbsp;<br>
</font><font face="Calibri" size=2>Allan Sindelar<br>
<a href="mailto:Allan@positiveenergysolar.com">
Allan@positiveenergysolar.com</a><br>
NABCEP Certified Photovoltaic Installer<br>
EE98J Journeyman Electrician<br>
Positive Energy, Inc.<br>
3201 Calle Marie<br>
Santa Fe</font>, New Mexico 87507<br>
<font face="Calibri" size=2>505 424-1112<br>
</font><a href="http://www.positiveenergysolar.com">
www.positiveenergysolar.com</a><br>
<hr>
<font face="Tahoma" size=2><b>From:</b>
re-wrenches-bounces@lists.re-wrenches.org
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of
</b>Dana<br>
<b>Sent:</b> Wednesday, July 01, 2009 5:20 PM<br>
<b>To:</b> 'RE-wrenches'<br>
<b>Subject:</b> [RE-wrenches] Fisher Paykal on a MAGNASINE<br>
</font><font face="Calibri" size=2>&nbsp;<br>
</font>Has anyone run a Fisher-Paykal washer on the Magna sine modified
sine wave 1200 watt inverter? Good to do or not?<br>
&nbsp;<br>
Thanks<br>
&nbsp;<br>
<font color="#1F497D">Dana Orzel</font></blockquote></body>
</html>