<html><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">Load sheding is not a bad idea if the tech exists. Not particularly complex either with networkable breakers and a smart controller in the inverter. Just software. Cost isn't an issue, they are willing to pay.<div><br></div><div>The issue on loads isn't battery cut-off (though that isn't a bad idea), but shedding the less-important loads to make sure the house does exceed the inverter power output. A 6kW inverter subpaneled will only give you about four 15 AMP circuits. However a typical house of this size will have 30 such circuits, yet good chance it won't be drawing much more than 50 AMPs for the whole house at any one time.&nbsp;How do you select what is important? Either the inverter is complicated or the&nbsp;electricians&nbsp;wiring is complicated.</div><div><div><br><div><br><div apple-content-edited="true"> <span class="Apple-style-span" style="border-collapse: separate; border-spacing: 0px 0px; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; text-align: auto; -khtml-text-decorations-in-effect: none; text-indent: 0px; -apple-text-size-adjust: auto; text-transform: none; orphans: 2; white-space: normal; widows: 2; word-spacing: 0px; "><div style="word-wrap: break-word; -khtml-nbsp-mode: space; -khtml-line-break: after-white-space; "><div>Troy Harvey</div><div>---------------------</div><div>Heliocentric</div><div>801-453-9434</div><div><a href="mailto:taharvey@heliocentric.org">taharvey@heliocentric.org</a></div></div><br class="Apple-interchange-newline"></span> </div><br><div><div>On Jun 23, 2009, at 10:01 PM, William Miller wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite"><div> <font size="3">Troy:<br><br> Let me guess... They want it right away and cheap, too.&nbsp; Generally speaking, this is an impractical request.&nbsp; Electrically operated circuit breakers or 20 A relays and controllers are expensive and complicated.&nbsp; One thing to learn in this trade is when to try and talk a client out of a bad idea, and when a client has such wacky ideas that it is best to walk away.<br><br> I could, however, suggest two ways to do this:<br><br> 1. Use two inverters and set the LBCO for one high.&nbsp; Connect one to critical loads and one (with the high LBCO) to non-critical loads.&nbsp; When the batteries start getting low, the non-critical-loads inverter shuts down, leaving the critical-loads inverter running.<br><br> Realize that you now need four load centers:&nbsp; Grid, generator (you have recommended a generator so they can use their wide screen TV during a wind storm, correct?), non-critical loads and critical loads.&nbsp; This type of design gets complicated fast.&nbsp; Will the AHJ be able to track this?&nbsp; Set a clause that allows you to collect hourly fees when they require three different meetings and three re-writes of the permit application.<br><br> 2. Use an Outback with external relays to shut off loads when the battery voltage falls below a certain point.&nbsp;&nbsp; This is a crude approach, the parameters are not flexible (hard coded delay values) and it requires custom built relay panels, time consuming, expensive and a potential service problem.<br><br> Either system is actuated on battery voltage rather than loads.&nbsp; Inverters I am familiar with have relays and internal controls that operate based a set-able battery voltages, but I know of none that has a programmable relay to actuate at a certain load level.&nbsp; In addition, loads change so rapidly that this type of switching would be erratic.&nbsp; Loading is a component of battery voltage, anyway, so you are including that indirectly.<br><br> Good Luck,<br><br> William Miller<br><br> <br><br> At 07:41 PM 6/23/2009, you wrote:<br> </font><blockquote type="cite" class="cite" cite=""><font size="3">Hi folks,<br><br> I need an inverter/charger/controller solution for a grid connect&nbsp; <br> house that:<br> 1. grid-connects (net-meters)<br> 2. Islands off of the battery in outages (whole house UPS)<br> 3. Feeds into the whole house breaker, so the whole house is backed up<br> 4. Shuts down less important breakers as needed, if the load for the&nbsp; <br> whole house is over the inverter limit<br><br> Instead of guessing which breakers are important to put on a battery&nbsp; <br> backed up sub-panel, my client would like the whole house backed up.&nbsp; <br> But of course, can't guarantee that the house won't be drawing too&nbsp; <br> much for a 6000 Watt inverter at any given time. So would like to have&nbsp; <br> the system intelligently remove less important breakers until the&nbsp; <br> system is below the inverter operation wattage.<br><br> Anyone know of a inverter system that is smart like that?<br><br> Troy Harvey<br> ---------------------<br> Heliocentric<br> 801-453-9434<br> <a href="mailto:taharvey@heliocentric.org">taharvey@heliocentric.org</a></font></blockquote></div>  _______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></blockquote></div><br></div></div></div></body></html>