William,<br>
<br>
Metal is only required from the point that the PV circuit enters the
building to the first accessible disconnect, outside the building
plastic is okay.&nbsp; For underground plastic is definitely best.&nbsp; Here the
inspectors have been happy with plastic being used inside the building
for 3 or 4 feet from the floor up to the disconnect.&nbsp; The rational is
that a fire fighter us not likely to cut through it.<br>
<br>
Yes, 100 volts isn't as much of a hazard as 400 to 600 volts.&nbsp; But it
is still a hazardous voltage and it makes nice arcs too.<br>
<br>
I believe most combiner boxes don't qualify as a disconnect device
because it takes a screw driver to open them before you can turn
anything off. <br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>
<br>
<br>
William Miller wrote:
<blockquote cite="mid:6.0.1.1.2.20090607173711.03af6ec0@millersolar.com"
 type="cite"><font size="3">Kent:<br>
  <br>
Interesting... <br>
  <br>
What if the array is ground mount?&nbsp; I prefer not to have metallic
conduit underground.&nbsp; Fortunately, for off-grid we often have a
combiner on the rack that qualifies for a disconnecting means.<br>
  <br>
Also, off-grid Voc is on the order of 100 volts, as opposed to 400 to
600.<br>
  <br>
William<br>
  <br>
  <br>
  <br>
At 04:01 PM 6/7/2009, you wrote:<br>
  </font>
  <blockquote type="cite" class="cite" cite=""><font size="3">William,<br>
    <br>
It is interesting that the 2008 code also has the
"utility-interactive" typo.&nbsp; None the less, it is
appropriate to put photovoltaic circuits in metal conduit for off grid
systems.&nbsp; The risk to fire fighters is nearly the same in both
cases.<br>
    <br>
Kent Osterberg<br>
Blue Mountain Solar<br>
    </font></blockquote>