<DIV><FONT size=2 face=Arial>I agree with Kelly and others that all grounding 
electrodes should be&nbsp;bonded together. My experience in lightning country 
with PV systems with&nbsp;a&nbsp;ground rod at the array and separate ground rod 
at the BOS&nbsp;and no wire connecting&nbsp; the ground rods has always resulted 
in fried equipment. The same systems, after they were repaired and the ground 
rods were connected together, survived every lightning storm for several 
years.&nbsp;I have found that the&nbsp;same holds true for any&nbsp;equipment or 
structure - good earth grounds all connected together create a grounding field 
and can create a cone of protection. Properly grounded equipment with all 
grounding electrodes connected together&nbsp;generally survive lightning storms 
and have been known to survive direct lightning strikes.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=bcrise@nietc.org href="mailto:bcrise@nietc.org">Brian Crise</A> 
</DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Friday, June 05, 2009 1:45 PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [RE-wrenches] 690.47D 
  (revisited)</DIV>
  <DIV><BR></DIV>Kelly,
  <DIV>It is my understanding that all types of grounding electrodes, 
  whether&nbsp;supplementary&nbsp;or not, for lightning protection or PV array 
  grounding shall be bonded together to form the grounding electrode system. 
  (250.106, 690.47(A) which sends you to 250.50, &nbsp; NFPA 780-2008 4.14). 
  &nbsp;If you do not do this and you do get a&nbsp;lightning&nbsp;strike or for 
  that matter any high frequency signal injected onto a grounding electrode you 
  will get what they call a ground potential rise onto one part of the system. 
  &nbsp;With the other&nbsp;separate&nbsp;grounding electrode not having this 
  same signal&nbsp;because&nbsp;of them not being common, you will have a 
  potential difference between the two&nbsp;separate&nbsp;electrodes even though 
  they are both in the ground. &nbsp;The ground (earth) is actually a very poor 
  conductor when it comes to high levels of high frequency current</DIV>
  <DIV>Hopefully this helps,</DIV>
  <DIV>Brian</DIV>
  <DIV><BR></DIV>
  <DIV>NABCEP Certified PV Installer</DIV>
  <DIV><BR></DIV>
  <DIV>To contact Brian L Crise:</DIV>
  <DIV>
  <DIV apple-content-edited="true"><SPAN 
  style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 12px Helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0" 
  class=Apple-style-span>
  <DIV 
  style="WORD-WRAP: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space"><SPAN 
  style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 12px Helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto" 
  class=Apple-style-span>
  <DIV 
  style="WORD-WRAP: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space">
  <P style="MARGIN: 0px; MIN-HEIGHT: 14px; FONT: 12px Helvetica"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Address:</FONT></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>16021 NE Airport Way</FONT></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Portland OR, 97230</FONT></P>
  <P style="MARGIN: 0px; MIN-HEIGHT: 14px; FONT: 12px Helvetica"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>Office Phone:<SPAN class=Apple-converted-space><SPAN 
  class=Apple-converted-tab>&nbsp; &nbsp;<SPAN 
  class=Apple-converted-space>&nbsp;</SPAN></SPAN></SPAN>(503) 262-9991 
  x.5054</FONT></P>
  <P style="MARGIN: 0px"><BR></P>
  <P style="MARGIN: 0px"><FONT style="FONT: 12px Helvetica" size=3 
  face=Helvetica>e-mail:<SPAN class=Apple-converted-space><SPAN 
  class=Apple-converted-tab>&nbsp; &nbsp;<SPAN 
  class=Apple-converted-space>&nbsp;</SPAN></SPAN></SPAN><A 
  href="mailto:bcrise@nietc.org">bcrise@nietc.org</A></FONT></P></DIV><BR 
  class=Apple-interchange-newline></SPAN></DIV></SPAN><BR 
  class=Apple-interchange-newline></DIV><BR>
  <DIV>
  <DIV>On Jun 5, 2009, at 12:10 PM, Kelly Keilwitz, Whidbey Sun &amp; Wind 
  wrote:</DIV><BR class=Apple-interchange-newline>
  <BLOCKQUOTE type="cite">
    <DIV>Mark, <BR>I don't think that the 690.47D "PV GE" is part of the 
    premises AC &amp; DC<BR>ground electrode system.<BR><BR>IMO, in order to 
    function to properly as enhanced protection from lightning<BR>induced 
    surges as described in the 690.47(D) section note in the 2008 
    NEC<BR>Handbook, the optional supplementary grounding electrode should not 
    be<BR>connected to the premises system AC and DC grounding electrodes, as 
    shown in<BR>Exhibit 690.6 of the Handbook. If an additional #8 (per 250.166) 
    is bonded<BR>to the premises AC/DC system GE, it's path will be parallel 
    with, and<BR>redundant to, the existing EGC. This could set up the potential 
    for an<BR>inductive ground loop, which might cause more damage to the system 
    during a<BR>lightning strike than it would prevent.<BR><BR>If the 
    additional electrode for array grounding (PV GE) of 690.47D is 
    not<BR>required, then the PV GEC of that section should not be 
    required.<BR><BR>Of course, these opinions are academic. What I really want 
    to know is what<BR>the AHJ's think! Any of you have to deal with this, 
    yet?<BR><BR>Thanks,<BR>-Kelly<BR><BR>Kelly Keilwitz, P.E.<BR>Whidbey Sun 
    &amp; Wind, LLC<BR>Renewable Energy Systems<BR>NABCEP Certified PV 
    Installer<BR>WA Electrical Administrator #KEILWKM923RB<BR>987 Wanamaker 
    Rd.<BR>Coupeville, WA, 98239<BR>360.678.7131<BR><A 
    href="mailto:sunwind@whidbeysunwind.com">sunwind@whidbeysunwind.com</A><BR>WA 
    Electrical Contractor #WHIDBSW920MS<BR>WA General Contractor 
    #WHIDBSW946M1<BR><BR><BR><BR><BR>On 6/5/09 10:01 AM, "Mark Frye" 
    &lt;markf@berkeleysolar.com&gt; wrote:<BR><BR>
    <BLOCKQUOTE type="cite">Kelly,<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">The question is, if the AJH had required you to 
      run the new array DC GEC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">directly to an additional DC array GE, would that 
      new DC GE system need to<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">be bonded with the exisitng AC GE system with a 
      bonding wire other than the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">new EGC running from the array to new DC 
    GE?<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Unfortunately, NEC 2008 is not clear about this 
      with respect to the new DC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">array GE. &nbsp;That leaves us with only the 
      general NEC requirement that all<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">premise GE's be bonded into a single 
    system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">So the total effect of the new 690.47D, assuming 
      that the "prcaticable"<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">location for the new DC array GE is not within 6 
      ft of the exisiting AC GE,<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">is this:<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">A new DC array GEC must run directly from the 
      array to a new DC GE system<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">and and a new bonding jumper must be run from the 
      new DC GE system to the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">exisitng AC GE system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">It the new DC GE system can be the same as the 
      existing AC GE by virtue of<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">it proximity (less than 6 ft) to the practiable 
      location, then the ne DC<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">array GEC must still be run directly to exist GE 
      system which is now the<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">AC/DC GE system.<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite"><BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Mark Frye<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Berkeley Solar Electric Systems<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">303 Redbud Way<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">Nevada City, &nbsp;CA 95959<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">(530) 401-8024<BR></BLOCKQUOTE>
    <BLOCKQUOTE type="cite">www.berkeleysolar.com<BR></BLOCKQUOTE>
    <BLOCKQUOTE 
    type="cite"><BR></BLOCKQUOTE><BR><BR>_______________________________________________<BR>List 
    sponsored by Home Power magazine<BR><BR>List Address: 
    RE-wrenches@lists.re-wrenches.org<BR><BR>Options &amp; 
    settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
    rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
    participant 
  bios:<BR>www.members.re-wrenches.org<BR><BR></DIV></BLOCKQUOTE></DIV><BR></DIV>
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options &amp; 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>