<html><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">Kelly,<div>It is my understanding that all types of grounding electrodes, whether&nbsp;supplementary&nbsp;or not, for lightning protection or PV array grounding shall be bonded together to form the grounding electrode system. (250.106, 690.47(A) which sends you to 250.50, &nbsp; NFPA 780-2008 4.14). &nbsp;If you do not do this and you do get a&nbsp;lightning&nbsp;strike or for that matter any high frequency signal injected onto a grounding electrode you will get what they call a ground potential rise onto one part of the system. &nbsp;With the other&nbsp;separate&nbsp;grounding electrode not having this same signal&nbsp;because&nbsp;of them not being common, you will have a potential difference between the two&nbsp;separate&nbsp;electrodes even though they are both in the ground. &nbsp;The ground (earth) is actually a very poor conductor when it comes to high levels of high frequency current</div><div>Hopefully this helps,</div><div>Brian</div><div><br></div><div>NABCEP Certified PV Installer</div><div><br></div><div>To contact Brian L Crise:</div><div><div apple-content-edited="true"><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-align: auto; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><span class="Apple-style-span" style="border-collapse: separate; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; -webkit-text-decorations-in-effect: none; text-indent: 0px; -webkit-text-size-adjust: auto; text-transform: none; orphans: 2; white-space: normal; widows: 2; word-spacing: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; font: normal normal normal 12px/normal Helvetica; min-height: 14px; "><br></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><font face="Helvetica" size="3" style="font: normal normal normal 12px/normal Helvetica; ">Address:</font></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><font face="Helvetica" size="3" style="font: normal normal normal 12px/normal Helvetica; ">16021 NE Airport Way</font></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><font face="Helvetica" size="3" style="font: normal normal normal 12px/normal Helvetica; ">Portland OR, 97230</font></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; font: normal normal normal 12px/normal Helvetica; min-height: 14px; "><br></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><font face="Helvetica" size="3" style="font: normal normal normal 12px/normal Helvetica; ">Office Phone:<span class="Apple-converted-space"><span class="Apple-converted-tab">&nbsp; &nbsp;<span class="Apple-converted-space">&nbsp;</span></span></span>(503) 262-9991 x.5054</font></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><br></p><p style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><font face="Helvetica" size="3" style="font: normal normal normal 12px/normal Helvetica; ">e-mail:<span class="Apple-converted-space"><span class="Apple-converted-tab">&nbsp; &nbsp;<span class="Apple-converted-space">&nbsp;</span></span></span><a href="mailto:bcrise@nietc.org">bcrise@nietc.org</a></font></p></div><br class="Apple-interchange-newline"></span></div></span><br class="Apple-interchange-newline"> </div><br><div><div>On Jun 5, 2009, at 12:10 PM, Kelly Keilwitz, Whidbey Sun &amp; Wind wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite"><div>Mark, <br>I don't think that the 690.47D "PV GE" is part of the premises AC &amp; DC<br>ground electrode system.<br><br>IMO, in order to function to properly as enhanced protection from lightning<br>induced surges as described in the 690.47(D) section note in the 2008 NEC<br>Handbook, the optional supplementary grounding electrode should not be<br>connected to the premises system AC and DC grounding electrodes, as shown in<br>Exhibit 690.6 of the Handbook. If an additional #8 (per 250.166) is bonded<br>to the premises AC/DC system GE, it's path will be parallel with, and<br>redundant to, the existing EGC. This could set up the potential for an<br>inductive ground loop, which might cause more damage to the system during a<br>lightning strike than it would prevent.<br><br>If the additional electrode for array grounding (PV GE) of 690.47D is not<br>required, then the PV GEC of that section should not be required.<br><br>Of course, these opinions are academic. What I really want to know is what<br>the AHJ's think! Any of you have to deal with this, yet?<br><br>Thanks,<br>-Kelly<br><br>Kelly Keilwitz, P.E.<br>Whidbey Sun &amp; Wind, LLC<br>Renewable Energy Systems<br>NABCEP Certified PV Installer<br>WA Electrical Administrator #KEILWKM923RB<br>987 Wanamaker Rd.<br>Coupeville, WA, 98239<br>360.678.7131<br><a href="mailto:sunwind@whidbeysunwind.com">sunwind@whidbeysunwind.com</a><br>WA Electrical Contractor #WHIDBSW920MS<br>WA General Contractor #WHIDBSW946M1<br><br><br><br><br>On 6/5/09 10:01 AM, "Mark Frye" &lt;markf@berkeleysolar.com&gt; wrote:<br><br><blockquote type="cite">Kelly,<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">The question is, if the AJH had required you to run the new array DC GEC<br></blockquote><blockquote type="cite">directly to an additional DC array GE, would that new DC GE system need to<br></blockquote><blockquote type="cite">be bonded with the exisitng AC GE system with a bonding wire other than the<br></blockquote><blockquote type="cite">new EGC running from the array to new DC GE?<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">Unfortunately, NEC 2008 is not clear about this with respect to the new DC<br></blockquote><blockquote type="cite">array GE. &nbsp;That leaves us with only the general NEC requirement that all<br></blockquote><blockquote type="cite">premise GE's be bonded into a single system.<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">So the total effect of the new 690.47D, assuming that the "prcaticable"<br></blockquote><blockquote type="cite">location for the new DC array GE is not within 6 ft of the exisiting AC GE,<br></blockquote><blockquote type="cite">is this:<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">A new DC array GEC must run directly from the array to a new DC GE system<br></blockquote><blockquote type="cite">and and a new bonding jumper must be run from the new DC GE system to the<br></blockquote><blockquote type="cite">exisitng AC GE system.<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">It the new DC GE system can be the same as the existing AC GE by virtue of<br></blockquote><blockquote type="cite">it proximity (less than 6 ft) to the practiable location, then the ne DC<br></blockquote><blockquote type="cite">array GEC must still be run directly to exist GE system which is now the<br></blockquote><blockquote type="cite">AC/DC GE system.<br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite"><br></blockquote><blockquote type="cite">Mark Frye<br></blockquote><blockquote type="cite">Berkeley Solar Electric Systems<br></blockquote><blockquote type="cite">303 Redbud Way<br></blockquote><blockquote type="cite">Nevada City, &nbsp;CA 95959<br></blockquote><blockquote type="cite">(530) 401-8024<br></blockquote><blockquote type="cite">www.berkeleysolar.com<br></blockquote><blockquote type="cite"><br></blockquote><br><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: RE-wrenches@lists.re-wrenches.org<br><br>Options &amp; settings:<br>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div></blockquote></div><br></div></body></html>