Hello Wrenches,<br><br>
We are working on a system with three Sunny Boy inverters that feed into
a system that is backed up by a generator.&nbsp; The inverters are
isolated from the generator by relays that open when the generator is in
the warm up stage, before connecting to the electrical
system.&nbsp;&nbsp; <br><br>
What is happening is that the breakers, that connect the inverters to the
grid, trip, .&nbsp; What is apparently happening is that an inductive
effect from the inverter's transformers is causing current rushs through
the breakers when the relays open.&nbsp; This only happens when the
generator is in exercise mode, when the grid is still up and the
inverters are operating. <br><br>
My theory is that it is much like the ignition system of an engine.&nbsp;
(For the example I'm using a system that still uses points).&nbsp; When
the points open, the voltage rises, because current will try to continue
flowing from an inductor. This raises the voltage to very high
levels.&nbsp; The resulting arc jumps the spark gap.&nbsp; <br><br>
I think that with the inverters, the high voltage causes a current surge
when the voltage reaches a potential where current will jump the gap in
the contactor. <br><br>
Has anyone experienced this?&nbsp; Have you found a good solution?&nbsp;
We could retrofit relays on the DC side, but this would not be
convenient.&nbsp; If we use DC relays, is there a downside to
that?&nbsp;&nbsp; Could we use the AC contactor to connect the inverter
output to a large capacitor to absorb the surge?&nbsp; Do we need faster
contactors with a bigger gap?&nbsp; Would the voltages hurt the
inverters? <br><br>
Thanks in advance, <br>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified PV Installer </font><font size=1 color="#0000FF">TM<br>
</font><font color="#0000FF">Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>