<font size=3>Brian:<br><br>
<br>
One more question:&nbsp; Why must the external transfer be &quot;rated
for at least 200 amp?&quot;&nbsp; The utility feed is 100 amp, the
generator is 82 amp and if my arithmetic is correct, the inverters can
generate 75 amps.<br><br>
William<br><br>
<br><br>
At 10:00 PM 4/28/2009, you wrote:<br><br>
<br>
<blockquote type=cite class=cite cite>William,<br>
&nbsp;<br>
In the Xantrex \u201cXW Power System Installation Guide\u201d, pages 2-34 to 2-37,
there is a parts list and some diagrams on the wiring of a 3-inverter
system. The parts list calls for two 5 ft (62\u201d hole-to-hole) 4/0 battery
cables to connect the third inverter up to the Distribution Panel.<br>
&nbsp;<br>
Also shown is the use of an external bypass switch to make up for the
lack of enough AC breaker spaces in a single Distribution Panel. It shows
a breaker/interlock panel, but a 2-pole manual transfer switch will also
work. Either way, it should be rated for at least 200A.<br>
&nbsp;<br>
Brian Teitelbaum<br>
AEE Solar<br>